furnace short cycling

I'm experiencing this like others. I cleaned the flame sensor, changed the filter, cleaned the evaporator coil, it was dirty, and still no change. Fires up, runs a few minutes, burners shut off, on the third try, it will relight, and it will do this for three cycles until it locks out. It's a Goodman GPG 10 single package gas-electric h & c unit, vintage 2005, the whole shebangs sits outside in the weather. Any chance it's my thermostat? I know it's a precision control, and last year I dropped it from about shoulder height, but it ran the AC all summer........thanks for your advice.
 
  #2  
Old 12-01-21, 10:33 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,035
Received 3,415 Upvotes on 3,063 Posts
That unit shows a control board with diagnostic LED. Have you checked that for a fault code ?
The board is usually located near where the power wiring enters.
There may be a sight glass in the door to look thru.
 
  #3  
Old 12-01-21, 10:38 AM
V
Member
Thread Starter
Join Date: Nov 2004
Location: USA
Posts: 163
Upvotes: 0
Received 1 Upvote on 1 Post
yes, it blinks once, and the owners manual says lockout due to failed ignition of flame dropout. The burners light for various amounts of minutes but never more than ten, and then the flame disappears.
 
  #4  
Old 12-01-21, 10:39 AM
V
Member
Thread Starter
Join Date: Nov 2004
Location: USA
Posts: 163
Upvotes: 0
Received 1 Upvote on 1 Post
burners fire up and then go out, relight and go out, three cycles before it locks out with the LED blinking, I should say
 
  #5  
Old 12-01-21, 10:43 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,035
Received 3,415 Upvotes on 3,063 Posts
You need to watch it when it first happens. After several attempts the code changes to lockout.
 
  #6  
Old 12-01-21, 11:00 AM
V
Member
Thread Starter
Join Date: Nov 2004
Location: USA
Posts: 163
Upvotes: 0
Received 1 Upvote on 1 Post
ok, I can do that. Are you saying watch the LED board when the flame disappears from the burners? I think I did that and it stayed steady red on, which is control ok is standby, call for heat, cool or fan modes in the owners manual. But I can watch it when it does its thing.
 
  #7  
Old 12-01-21, 11:27 AM
V
Member
Thread Starter
Join Date: Nov 2004
Location: USA
Posts: 163
Upvotes: 0
Received 1 Upvote on 1 Post
ok, when the flame disappeared from the burner, the red light was just steady on; when it failed to light on the third try, it started to flash, but it was just one flash. the owners manual says there's .25 second flash on, then .25 second off, and a full 2 seconds in between, and I'm reading just one flash

the owners manual:
a red led light is provided to indicate system fault as follows
Steady On control ok
Stead Off no power
1 flash lockout due to failed ignition or flame dropouts
2 flashes open end switch
3 flashes end switch closed without induced fan motor on
4 flashes limit switch is open
5 flashes flame detected with gas valve closed
6 flashes compressor output delayed from short cycle/staging timer

I'm pretty sure I'm reading it correctly, .25 seconds is a short flash, and then 2 full seconds in between...
 
  #8  
Old 12-01-21, 11:34 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,035
Received 3,415 Upvotes on 3,063 Posts
Page 14 starts discussion on troubleshooting. A fairly common problem is burner rust inside the burner especially with a packaged unit that is outside in the weather. The burners would be taken out and at least blown out.

If you observe the flames they need to hit and engulf the flame sensor rid fairly quickly.
You may need to monitor the flame rod current for an issue.

Goodman GPG 10 downloadable manual
 
  #9  
Old 12-01-21, 11:50 AM
V
Member
Thread Starter
Join Date: Nov 2004
Location: USA
Posts: 163
Upvotes: 0
Received 1 Upvote on 1 Post
thanks, Pete. I guess I'm seeing some flame "rollout" but I wouldn't say it was a whole lot. It's intermittent. Inside the exchanger, it looks like there's some type of screen, and that's all orange when the burners are lit. With that description, would you think taking the burners out and hitting them with a wire brush and blowing them out would be the fix? In your opinion. Thanks again.
 
  #10  
Old 12-01-21, 11:58 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,035
Received 3,415 Upvotes on 3,063 Posts
Based on servicing packaged units.... yes... clean the burners.
Clean the burner orifices too.
 
  #11  
Old 12-02-21, 06:49 AM
V
Member
Thread Starter
Join Date: Nov 2004
Location: USA
Posts: 163
Upvotes: 0
Received 1 Upvote on 1 Post
Hello, good morning
I cleaned the burners and orifices, they really weren't dirty, actually, but I put a wire brush on them. I used to line cook in a restaurant, cooked on gas, feel qualified to offer my opinion on whats a dirty burner. Man, those were the days!
Cleaned the orifices too. No change. This unit has a 20 year Heat X warranty, I suppose the issue there would be is there a part available these days.

Next step call in a contractor?? Thx
 
  #12  
Old 12-12-21, 04:50 PM
N
Member
Join Date: Apr 2011
Location: usa
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Gee.. i have exact same issue. the difference is that i have no error code coming out. the light on the board is solid and it does not locked out. Mine runs about 3 mins and stops before it reaches the temp. I am not sure what to look for.
 
 