Hi. I have a 6" oval duct running in a joist bay that I need to split in two and run oval ducts across the joists to supply two vents in the basement suspended ceiling. I searched online and have not found an "oval tee". I am thinking of attaching an oval start collar on top of a piece of oval pipe to make myself a tee. It would look something like the attached picture.
Looking for thoughts on
- Will there be an air flow issue with this home made "oval tee"?
- If I buy a round full flow tee and squish the round ends into ovals, will that work?
Thank you
Last edited by PJmax; 12-15-21 at 06:31 PM.
Reason: reoriented/enlarged pic
You can always make your own starting collars if you have trouble finding an oval one.
I will warn though, a 6" oval duct is usually used for a single vent. The fact that you're tapping 2 more vents off it raises a flag that you might have a lot less airflow (and therefore heat) than you need or expect, especially if you're heating the basement tapping off a first floor duct. Just making sure you've considered it.
Zorfdt, thanks for the heads-up. The 6" oval is directly connected to the main trunk, it's not a tap on another 6" oval. I understand there will be less air flow in each of the two vents. But the basement has two additional supply vents. Both are directly connected to the main supply trunk. I have been monitoring the temperature and It's already cozy in the basement with just those two supply vents. So I am not too concerned.
Furnace is ICP GUK050N12C1, 22 yrs old.
The resistance igniter stays on (red hot) as long as the furnace works, as does the small flame between the burners that is used to light up the main burners.
It may be that the small flame also heats up the area where the flame roll-out switch is located.
70 year olf natural gas furnace - 100,000 btu won' start - replaced thermocouple - still won't
Repair guy suggests pilot safety valve.. Honeywell... ???