Rheem gas furnace runs with no flame


  #1  
Old 12-28-21, 12:53 PM
E
Member
Thread Starter
Join Date: Dec 2021
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Rheem gas furnace runs with no flame

I have a Rheem Criterion gas furnace. It runs fine and has been serviced recently. They were not able to solve this either.
The furnace runs fine on a heat call, but then the fan(main blower) will run after the flame is out. I know it is supposed to do this at the end of the heat call for cool down, but this is not that. When I open and close the door, tripping the lockout, it fires up again with flame and can then run for some time without doing it again. 2 green LED's are lit when in normal operation, but only 1 is lit when this occurs. Bad Board? Gas valve? very intermittent but not trustworthy. I could leave home and the fan could run all day doing nothing.Flame sensor has been replaced along with the ignitor. Please help!!!


Reference thread: trane-furnace-flame-turning-off.
 

Last edited by PJmax; 12-28-21 at 01:55 PM. Reason: added reference thread
  #2  
Old 12-28-21, 02:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,067
Received 3,422 Upvotes on 3,068 Posts
Welcome to the forums.

I didn't leave your question posted in that other thread. Doing so means double replies and questions.

The fault codes should be listed on the back of the blower door.
I believe what you are seeing is a one hour lockout code.
That means a fault had happened.... probably several times and then the board locked out.

That furnace blower is timer controlled from the control board.
You need to reset the furnace and watch it until failure to get the actual fault code.
Your furnace may have code storage.
I need the full model number for that or the part number off the control board.
The furnace model is on the ID tag inside on the side wall near the burner.
 
  #3  
Old 01-04-22, 02:13 PM
E
Member
Thread Starter
Join Date: Dec 2021
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hi Pete;
Thank-you so much for the reply. the only problem with trying to watch when it fails is that it can go for a day or so before it does it again. I have heard it happen when in the room, you can hear the flame go out. When I look through the site glass (that I had to install) I see 2 led's lit when running/normal/off. When it fails and is just blowing air, 1 LED is lit (the power LED) the one that is out has an "ok" label. I will get the stuff you asked for. I do have some pics of the board, I will try to post them here. Here are some #'s off the board: 1012-823, 922613,
thanks again for all of your help.



this is my board. Should I replace it or is it something else?

Chris

 
 