Lincoln Barriere furnace LB0-DR blower
My furnace fires up, runs 2-4 minutes, shuts off, blower does not come on.
#2
Welcome to the forums.
Your oil fired furnace has a fan/limit switch that controls the blower in heat mode.
It is explained in this thread.... Lincoln Barriere LBO 105-DR oil furnace questions
If your furnace is shutting down after 3-4 minutes that sounds like it's overheating. That means the fan/limit switch is probably ok and you have a problem with the blower motor.