Blower motor still won't start after replacing motor and capacitor
Blower motor still won't start after replacing motor and capacitorI have an WeatherKing furnance (Rheem mfr co. RCBA-3765GH21XI;2004) gas furnace. The blower fan wasn't starting and making humming noise and smell of burning so I replaced it with brand new motor and brand new capacitor. Exact same brand/model/etc (5KCP39RGS935S - OEM Upgraded Replacement for GE Blower Motor 51-23017-42 115v)
. The thermostat settings are checked and on Heat (higher temp with Fan Auto mode). Even tried resetting via turning ON/OFF furnace switch in the circuit breaker.
Upon manually turning the switch ON, all the initial starting steps work up until its time for the blower to come on. Once new motor was installed it does not make humming noise anymore but it does not even start the fan. The motor fan blower works fine (meaning the shaft is moving OK in circular motion) if try testing outside (not installed in the housing). This is the 2nd motor I have changed thinking 1st one was faulty.
Anything I could be missing? Any help or guidance is appreciated. Blower Motor Circuit 1 Flame and Draft Motor Inducer Chamber Blower Motor circuit2 Blower Motor Housing Blower Motor fan working outside the housing Specifications
Can’t tell much from that pic, how is the fan running on the floor? What are the 2 blower circuits ? One thing you might try is reseating all of those plug connectors make sure the terminals are clean and tight.
Geo 🇺🇸
That looks like an ICM 288 1/3 control board.
If you look where the blower wires connect it should be labeled fairly clearly.
I know your board has a blower COOL and a blower HEAT connection.
It may or may not have a blower FAN connection. The newer boards have it.
I can't see your diagram clearly.
So... looking at the picture below. The motor neutral needs to be on any one of the neutral terminals.
The motor high speed.... cooling.... needs to be on the blue cool terminal.
The motor medium speed..... heating.... needs to be on the red heat terminal.
You can use any remaining motor speed wire on the yellow terminal if available.
You need to use the blower speeds that match your system.
Typically A/C uses the highest speed and heat uses medium or medium/high.
First off please, my heater is capable of handling twice the entire 1500 sf house including the basement which it originally heated; remodeled 4 years ago and added new intake, trunk, simplifying runs, tying old with new but same plant (20 yrs). I'm trying to figure out basically 2 things, reducing the amount of drop up and venting the entire room which will have a bathroom. The video shows the trunk and the runs to the left and at the first 90 which then 90's up to the kitchen above.
1) Can I get that run up to the kitchen tighter to the ceiling?
2) I need to heat the bathroom area and the rest of the room. I was thinking of adding a vent to the trunk but wasn't sure about where to put one in the bathroom. I'm building a soffit and plan on adding a fan to that so maybe I should put the vent in-between the 2 90's?
Any advice is appreciated.
[url=https://www.youtube.com/watch?v=C9LZoN06aNk]Basement video[/url]