Help w/ Old Bryant Furnace / Fan Won't Come On


  #1  
Old 09-03-22, 07:48 AM
T
Member
Thread Starter
Join Date: Dec 2015
Location: usa
Posts: 17
Upvotes: 0
Received 0 Upvotes on 0 Posts
Help w/ Old Bryant Furnace / Fan Won't Come On

Hi, Friends,

I have an old Bryant furnace here that's mostly very reliable. It's a model 394GAW036100

She'll make heat when called for but even after a good long while fan will not come on. A bunch of years back fan wouldn't turn OFF so I replaced PC board which solved that problem. I recently changed PC board AGAIN but fan still will not come on.

Winter's coming ; ) I'd sincerely appreciate some guidance.

THANK YOU!
Mike in MA
 
  #2  
Old 09-03-22, 10:34 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,087
Received 3,422 Upvotes on 3,068 Posts
What is the part number on the board ?
What does FAN ON do ?

You should have provisions for a HEAT and COOL selection on the board.
Try swapping them.
 
  #3  
Old 09-03-22, 02:37 PM
T
Member
Thread Starter
Join Date: Dec 2015
Location: usa
Posts: 17
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the comeback ..

This is an <old> furnace ie no Cool selection.
Here's a pic of board that'll hopefully help.

Best, Mike

 

Last edited by PJmax; 09-04-22 at 11:41 AM. Reason: labeled picture
  #4  
Old 09-03-22, 03:26 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,087
Received 3,422 Upvotes on 3,068 Posts
That's an older Carrier/Bryant board.....HH84AA011
That would mean your furnace is around 30 years old.
Furnaces don't live forever. Be sure to have the heat exchanger checked for rust thru.

The heat blower is directly controlled via a timer on the board.
It should be 75 seconds on and 105 seconds off.

G is the abbreviation for blower.
That has Gc for cooling blower speed and Gh for heating blower speed.
Black blower wire for high speed cooling is on HI terminal.
Red blower wire for low/medium speed heating is on LO terminal.
White blower wire is on COM.

Try a jumper from R to Gc. The relay should click and the blower will start on high.
 

Last edited by PJmax; 09-06-22 at 10:08 AM. Reason: correction
  #5  
Old 09-03-22, 03:55 PM
T
Member
Thread Starter
Join Date: Dec 2015
Location: usa
Posts: 17
Upvotes: 0
Received 0 Upvotes on 0 Posts
This is great and thanks for clearing up heat and cool speeds.

So to be clear "R" is the red wire attached to LO terminal?
I'm jumping this red wire to terminal Gc and Gh to see if fan runs?
iow jumping LO to Gc and Gh?

There's also a terminal labeled "R"

Thanks!
M

 
  #6  
Old 09-04-22, 11:44 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,087
Received 3,422 Upvotes on 3,068 Posts
Labeled your picture.

The high voltage wires go to the blower. Nothing gets jumpered there.

You want to jumper from the R terminal to Gc.
You can just hold the jumper in place. No need to put it under the screw terminals.
 

Last edited by PJmax; 09-06-22 at 10:09 AM. Reason: correction
  #7  
Old 09-04-22, 05:58 PM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 1,799
Received 52 Upvotes on 46 Posts
There's no point of doing any troubleshooting without first pulling the blower assembly and visually inspecting the heat exchanger for cracks, holes and rust.
The probability that this furnace is still safe to run is very low unless you're in the south and it has barely run.

Even if hxt still okay, if your area gets real winters you should get a new furnace over repairing yours, as yours is only 60 to 70% efficient. The ignition control system is also obsolete and parts are not commonly available.

Jumpering from R to gc would test the motor in continuous mode.

Do you have a multi-meter?

 
  #8  
Old 09-04-22, 06:39 PM
T
Member
Thread Starter
Join Date: Dec 2015
Location: usa
Posts: 17
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you, Fellas'

We're in MA, I understand that a new furnace is a must and I will begin investigating by reaching out to Mass Save. We just finished an 8 month to-the-studs renovation of our 2nd floor apartment and we're <really> not in a good spot to get a new furnace, I'd like to try to get through this winter if at all possible.

Based on what you wrote I take it blower has to come out to get a look at HXR?

As far as blower goes I'll jump R to Gc and Gh tomorrow.
- If blower runs?
- If I get nothing?
I do have a multimeter btw.

Thanks again I do you appreciate y'alls expertise,
Mike
 
  #9  
Old 09-05-22, 06:07 AM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 1,799
Received 52 Upvotes on 46 Posts
It's R to Gc only.

If the fan runs, it means the tap used for cooling and continuous fan works.
Would need to go in with a meter and see if in heating mode, it is energizing the heating fan terminal 75 seconds after the burners light.

If it isn't, need to see if power is present on Gas-3 terminal on the board when the main burner is on - if you have power there and fan isn't timing on, board is defective.

I can get more specific later.

The heat exchanger can be partially inspected from the burner inlets, but to get a good view of all of it, need to inspect from the top or bottom -> so blower removed or access hole cut into plenum above, if there's no a/c coil directly on top of the furnace.
If the heat exchanger is compromised, you must replace the furnace before winter.

----------------
When replacing the furnace, if windows have been changed and or insulation added, should downsize it.
Even if not, many furnaces are over-sized.
 
  #10  
Old 09-05-22, 12:09 PM
T
Member
Thread Starter
Join Date: Dec 2015
Location: usa
Posts: 17
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok .. main burner's on and I let it run awhile: when I jump R and Gc, relay clicks but fan doesn't come on.

When main burner has just lit V at Gas 3 is zero. When burner has been running for awhile V reads 60 mv which is weird right?
How much voltage should be present at Gas 3?

Thanks,
Mike
 

Last edited by TheGuitarFairy; 09-05-22 at 02:01 PM.
  #11  
Old 09-05-22, 04:42 PM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 1,799
Received 52 Upvotes on 46 Posts
Did you check with that wire connected, or disconnected?
Would need to be connected, or check wire itself, not board with it disconnected.
Did you set your meter to AC volts? That's where it needs to be, not dc.
One meter lead needs to be on common to complete the circuit.

Now, based on the fact cooling relay clicks but fan doesn't come on though, should jump right to seeing if board is applying to heating terminal.

After 75 seconds of burner on time, check for line voltage (120v ac +/-) between Lo and Common on board.

If there's power, you have a bad motor -> the motor in your furnace doesn't use a capacitor.
If there isn't, need to check for power again at gas-3.

BTW without fan running in heating mode, high limit should trip and shut off burners.

Please do not ignore advice to check heat exchanger - if it's bad, you can not run it another season, the furnace must be replaced before fall.
 
  #12  
Old 09-05-22, 09:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,087
Received 3,422 Upvotes on 3,068 Posts
My mistake.... this furnace blower motor does not use a capacitor as I previously mentioned.
 

Last edited by PJmax; 09-06-22 at 10:25 AM. Reason: correction
  #13  
Old 09-06-22, 04:43 AM
T
Member
Thread Starter
Join Date: Dec 2015
Location: usa
Posts: 17
Upvotes: 0
Received 0 Upvotes on 0 Posts
My meter is digital
I can't find a capacitor, I don't think there is one.
Motor spins freely by hand, no resistance

- With burners running I checked V between C screw terminal and Gas 3 w/ wire still attached to board and was getting that reading in the mv's.
- Also checked V between C and <G3 wire> w wire off G3 and got same mv reading.
- After burner was running 75 second I checked V between Lo (terminal on board) and C terminal and also got a V in the mv's
- W/o fan running high limit did turn off burners eventually.

Thanks you, Fellas,
Mike

edit PS .. put a call in to HVAC tradesman, waiting to hear back. Just 'cause it's my nature I would like to figure this blower thing out ; )
- thank you again for the help and sharing your knowledge like this.
 

Last edited by TheGuitarFairy; 09-06-22 at 05:39 AM.
  #14  
Old 09-06-22, 10:23 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,087
Received 3,422 Upvotes on 3,068 Posts
I came across the correct wiring diagram.
There is no capacitor shown.
R is jumpered to Gh at the low voltage connection.

I labeled the three high voltage wires.
You need to check between the white and red wire for 120vac when the blower should be running.

 
  #15  
Old 09-06-22, 01:12 PM
T
Member
Thread Starter
Join Date: Dec 2015
Location: usa
Posts: 17
Upvotes: 0
Received 0 Upvotes on 0 Posts
After letting burner run for 2mins I'm not getting anything between White and Red wire.
 
 