Trane xl 90 burner replacement: where to purchase
#2
In your first thread I mentioned the importance of a model number. XL90 is not a model number.
Look on the inside wall of the furnace near the burner area for the ID tag.
Post the entire model number.
That burner doesn't look familiar....especially for a Trane.
Keep in mind that older furnaces need to have their heat exchangers checked for rust thru issues.
Rust thru allows CO to enter the air stream and get carried into the house.
Are you sure that's not a Goodman burner ?
It looks identical to a B1822501S.
B1822501S image search
Look on the inside wall of the furnace near the burner area for the ID tag.
Post the entire model number.
That burner doesn't look familiar....especially for a Trane.
Keep in mind that older furnaces need to have their heat exchangers checked for rust thru issues.
Rust thru allows CO to enter the air stream and get carried into the house.
Are you sure that's not a Goodman burner ?
It looks identical to a B1822501S.
B1822501S image search
Houston204,
muncho
voted this post useful.
#3
Member
Thread Starter
CERTIFIED
MODEL NO,
TUCICOB960A0
INPUT
1002.0010 BTU/HR.
TEMP. RISE °F
FROM
25 TO
VOLTS/PHASE/HERTZ
ANS 221. 470
FOR INDOOR INSTALLATIO
CONSTRUCTED ON SITE.
SERIAL NO.
LIMIT SETTING
1 Cr
°F
MAX. EXT, STATIC PR
INCHES W
TOTAL AMPS
MANIFOLD PRESSURE
(IN INCHES OF WATER)
FLAME
IF
nGCSXC
ROLLO
NAT.
•5 LP. 10.5
TH
SUPPLY PRESSURE
(IN iNCHES OF WATER)
MAX. NAT. 10,5, L P 13.0
MIN.NAT.
4,. 5L P 11.0 FOR PURPOSE OF II
TYPE FSP FERCED
ATR
MODEL NO,
TUCICOB960A0
INPUT
1002.0010 BTU/HR.
TEMP. RISE °F
FROM
25 TO
VOLTS/PHASE/HERTZ
ANS 221. 470
FOR INDOOR INSTALLATIO
CONSTRUCTED ON SITE.
SERIAL NO.
LIMIT SETTING
1 Cr
°F
MAX. EXT, STATIC PR
INCHES W
TOTAL AMPS
MANIFOLD PRESSURE
(IN INCHES OF WATER)
FLAME
IF
nGCSXC
ROLLO
NAT.
•5 LP. 10.5
TH
SUPPLY PRESSURE
(IN iNCHES OF WATER)
MAX. NAT. 10,5, L P 13.0
MIN.NAT.
4,. 5L P 11.0 FOR PURPOSE OF II
TYPE FSP FERCED
ATR
#4
Member
Thread Starter
#6
Member
Thread Starter
#7
You're only showing the inside of the burner.... not the entire assembly.
Your model.... TUC100B960A0
Burner # BNR00567
The burner is no longer shown in the Trane parts list. Furnace is too old. (1989)
May be time to replace the furnace.
I've only found what I think is your burner. Better sit down before looking at the price.
Repair Clinic parts
If no luck at Repair Clinic try HVAC PartsShop..... HVAC PartShop
Your model.... TUC100B960A0
Burner # BNR00567
The burner is no longer shown in the Trane parts list. Furnace is too old. (1989)
May be time to replace the furnace.
I've only found what I think is your burner. Better sit down before looking at the price.
Repair Clinic parts
If no luck at Repair Clinic try HVAC PartsShop..... HVAC PartShop
#8
Member
Thread Starter
I am just needing the 3 cluster burner tubes would the Goodman ones work if same measurement as trane
#9
Quite honestly I've never had to change a burner before. Have cleaned many.
If the measurements are the same it should work.
Doubtful there are too many burner manufacturers.
If the measurements are the same it should work.
Doubtful there are too many burner manufacturers.
muncho