Mr. Heater will not Start


  #1  
Old 01-16-24, 09:01 AM
W
Member
Thread Starter
Join Date: Jan 2024
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Mr. Heater will not Start

I have a Mr. Heater Max 50,000 BTU garage heater that has been working for years until now. When the t-stat call for heat nothing happens except for the LED flashing 3 times. I understand it's the pressure switch and it sounds as if the pressure switch failed to close before CAB is energized. So, the question is: How do I repair this? Is it the electrical switch on the pressure switch bad, or is there another issue?

Thanks in advance for any and all help!
Bill
 
  #2  
Old 01-16-24, 10:45 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,985
Received 4,152 Upvotes on 3,729 Posts
Welcome to the forums.

Please post the model number for that heater.
There are too many different sub models.

If it has a pressure switch then it must have a draft inducer.
The draft inducer should be the first thing that starts on a call for heat.
 
  #3  
Old 01-16-24, 01:47 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,532
Received 95 Upvotes on 88 Posts
3 flashes - Pressure switch failed closed before CAB is energized or failed open after CAB is energized

If the pressure switch is stuck closed it will be a cheaper fix than inducer or board failure.
Unplug one of the 2 wires to the pressure switch to see if the inducer will run.

is the model a MHU50 ?

 
  #4  
Old 01-16-24, 03:24 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,985
Received 4,152 Upvotes on 3,729 Posts
Not needed.
 
 