Frozen coils inside

My Central Air System coils are frozen on the bottom. I have changed the filter, cleaned the fins, the outside coils are a little clogged but no more than normal. Is there anything else I can check before calling a service tech?
 
Sponsored Links
  #2  
Old 04-04-02, 03:34 PM
PDF
Visiting Guest
Posts: n/a
If you are getting

cooling and the unit cycles on and off----your drain is plugged.The water stands in the drain pan,then the freon freezes it.If your a/c is not cooling right you are low on charge or have air flow problems.Shut system down,place tstat to fan on position and see if the drain from unit drains.PDF
 
  #3  
Old 04-04-02, 10:12 PM
jonathanisaac's Avatar
Member
Join Date: Feb 2002
Location: Earth
Posts: 224
Received 0 Votes on 0 Posts
---------------------------------------------------
 

Last edited by jonathanisaac; 08-04-06 at 09:48 PM.
  #4  
Old 04-05-02, 09:57 AM
HVAC Oracle
Visiting Guest
Posts: n/a
Frozen Coils

The evaporator coil above your furnace should be @ 45F, well above the freezing point. If there is any ice forming on the coil then there is a problem. Air flow or refrigerant.
The air flow can be tested by measuring the temperature drop (TD) across the coil. It should be 15F to 20F, a higher TD indicates a lack of air flow. This can be caused by dirty filters, dirty supply fan, plugged evaporator coil. This is why your AC needs to be checked every month, keep the filter clean to prevent this type of problem, if your filters have ever been negelected, this could be the cuase of the freezing. Air flow is also effected by ductwork size, and supply and return air grills.

This other cause of freezing is from the refrigerant. If the system is undercharged or the refrigerant is not being properly feed to the evaporator, then the coil temperature will drop below 32F and cause freezing. A low TD across the evaporator or a Warm suction line (big pipe at the furnace normally 55F to 60F) or a Cold liquid line (little pipe at the furnace normall 70F to 90F ) indicate a refrigerant problem and would require the services of a qualified technician.

HVAC Oracle
 
  #5  
Old 04-05-02, 10:47 AM
joelp
Visiting Guest
Posts: n/a
Freeze up is normally a result of refrigerant loss. Eventually you will build enough ice up that you will not be able to pass air through the coil. Get it serviced, and find the leak.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: