Question a/c

i have water coming in ceiling,and drain has hardly ever had water drain.the plenum is water soaked?
 
Sponsored Links
  #2  
Old 05-09-02, 11:56 AM
ahasbeen
Visiting Guest
Posts: n/a
Have to assume your ahu is in the attic. Either the drain is plugged at the drain pan, at the trap or in th drain line itself (a double "trap" maybe?) If you have a pan under the unit then the float limit switch may be kaput
 
  #3  
Old 05-09-02, 06:04 PM
hvac4u's Avatar
Member
Join Date: Aug 2001
Location: NW atlanta
Posts: 3,147
Received 0 Votes on 0 Posts
cut the drain

blow it out, if problem persists evap drain pan may be rusted through, how old?
 
  #4  
Old 05-11-02, 05:11 AM
bruce wayne
Visiting Guest
Posts: n/a
hvac4u

has been blown out.unit is 24?does not really look like pan is rusted through.3 tech's have looked,no mention of that problem.all want to replace unit.



thanks,
bruce
 
  #5  
Old 05-11-02, 07:52 AM
hvac4u's Avatar
Member
Join Date: Aug 2001
Location: NW atlanta
Posts: 3,147
Received 0 Votes on 0 Posts
24 years old ?

take the cover off the coil compartment, and check the pan. if no one has disturbed the coil (repositioned it, maybe if changing the furnace) my money is on rusted pan. if unit were freezing up, due most likely to low charge or restricted airflow, water will overflow the pan......but 24 yrs old, i still say the pan....let us know
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: