Question A/C not working properly

My A/C fan is running, but you feel no air coming out of the vents. The compressor was replaced just last summer. It seems like the fan is only running and nothing else. Please give me some suggestions since it is a holiday(of all the days for it to go out!) none of the A/C repairmen are working.
 
Sponsored Links
  #2  
Old 05-27-02, 08:40 AM
hvac4u's Avatar
Member
Join Date: Aug 2001
Location: NW atlanta
Posts: 3,147
sounds like restricted airflow

this scenerio (customer says no airflow with a/c on) generally ends up with a frozen evap coil, caused by lack of airflow,....filter or blocked return, dirty blower wheel, dirty evap, or low refrigerant charge
 