Airconditioning

Reply

  #1  
Old 05-27-02, 07:44 AM
ekalb66
Visiting Guest
Posts: n/a
Angry Airconditioning

I have a rheem seer 10, the furnace in the house runs on cool, but i do not notice the outside unit running, the relay does ingage when the unit is turned on, but the fan in outside unit doesnt run, what do u think i can do without calling in a tech.

thanks
 
Sponsored Links
  #2  
Old 05-27-02, 08:09 AM
sandman6778
Visiting Guest
Posts: n/a
try spinning outdoor fan by hand . If fan motor runs you need a new capacitor. also be sure compressor is running.if you have no air coming out of supply ducts in house you probably need to replace filter.That is if indoor fan is running.
 
  #3  
Old 05-27-02, 08:47 AM
hvac4u's Avatar
Member
Join Date: Aug 2001
Location: NW atlanta
Posts: 3,147
Received 0 Votes on 0 Posts
if relay

engagerd means contactor recieving 24 volts, and pulled in, be sure that your voltage is going across these points. is compressor is running with no fan either burnt wire, bad cap or fan. if compressor is not running, and you are getting 240 volts across contactor, check for dual cap that runs both comp and fan. be sure you have 240 outside, if you lost one leg, would also have these symptoms. if i confused you let me know, good luck
--------------------------------

happy memorial day
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: