bought a honeywell rectangular lever type t stat. my question is about the heat antisipator what number should this be set at so the furnace can kick on. thanks.
#2
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote
on
1 Post
What was the old tstat set at ???????? Might look on the gas valve some of them say. The antisipator is not like to turn the furnace on. it more like how long will it run after the tstat turns it on. If the furnace heats up the room more than the tstat is set for push the antisipator back a little for a shorter run. If it dont get up to the heat set on the tstat push it up a little for a longer run.