DUCANE heat pump

I recently installed a DUCANE heatpump and the electric heat is comming on with the A/C. There is a jumper wire on the stat from w1 to y the connections on the stat are

W1 W2 C Y O R G the connections on the furnace are

W1 W2 C R G in the installers manual it tells me to hook both w1 and w2 from the furnace to the w on the stat but when these wires are connected the electric heat is powered think i imght have to pull the jumper on the stat and split my w1 and w2 from the stat to the furnace??????????? Any of this sound correct? Any hints helpfull!!
 
Sponsored Links
  #2  
Old 09-08-04, 08:02 AM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,386
Received 0 Votes on 0 Posts
You dont say what tstat but like on a CT3611 you have to have the Y to W1 jumper on
 
  #3  
Old 07-31-07, 12:44 PM
C
Member
Join Date: Dec 2006
Posts: 8
Received 0 Votes on 0 Posts
Heat pump problem

The y on the thermostat activates the compressor, either for heat or for AC.
Depending upon how your airhandler is wired, the W1 should activate the electric heat when needed. If it is jumped to y, it is coming on whenever you call for heat or AC. This is not correct. You should disconnect the jumper and ensure that the W1 connection does indeed feed the electric heat relay or sequencer.

The o terminal is usually the activator for the reversing valve and w2 is to
the second stage heat.

How many KW of electric heat do you have?
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: