New Thermostat Wiring Problem
Old 09-23-04, 01:36 PM
Itry
I have a Carrier 2 stage Heat Pump. I have a problem after changing thermostat from Totalline to Ritetemp 8085C.
Hereís the setup:
Heat pump was move 3 years ago. My technician had to splice the wire going to the outside unit. He did not connect every wire. Every thing has worked OK, i.e. Heat w/aux, and Cool until I changed the thermostat.
Wires at the splice:
From outside unit Splice Totaline thermostat Ritetemp thermostat connections connections
Red ------------------Red-----------------R----------------R
White-----------------White---------------E------------Not connected
Yellow----------------Yellow---------------Y1--------------Y
Orange----------------Orange--------------O---------------O
Black------------------Brown- ------------C---------------C
Blue------------------- W2
Green------------------ G
Brown----------------- X
As you can see, the Blue, Green, and Brown were not connected at the splice. And, the Black from the outside unit was connected to the Brown at the splice? Also, the E was not connected at the Ritetemp as the instructions said to tape it off.
When I turned the unit on cool, the outside unit ran but the fan did not. So I connected the Green wires at the splice and connected the Green wire to the G terminal at the Ritetemp. Cool and fan worked.
I tried Heat. Heat worked and fan worked, but the Aux/Emergency strips were always on.
I called Ritetemp for assistance, they said the Blue wire needed to be connected at the splice and then connected to the W2 on the Ritetemp. I did that and same results. Heat and fan works but the Aux/Emergency strips are still on.
Any advice on how to get the Aux/Emergency to only come on when it is needed?
Old 09-24-04, 01:53 PM
Ed Imeduc's Avatar
Received 1 Upvote on 1 Post
Wink
Id say you have to check out the wires here for sure.
C -common R- power Y1 -compressor first stage Y2 compressor 2 stage W1 -Stage 1 heat
W2 Auxiliary heat relay G-Fan relay O cooling relay B heating relay You only tie one O or B E Emergency
ED
Old 10-10-04, 05:30 PM
Itry
Figured it out....went outside to the outdoor unit, read the wiring diagram, found the white wire was the W2 so I attached the White wire to the W2 terminal on the thermostat and everything works.