i have a amana heat pump that is about 1yr old.......it worked fine last winter but this year i cant get the outdoor unit to come on at all......if i go out and engage the contactor manually it all come on and works fine as long as i hold the contactor in but that is a very good solution to my problem lol.......just a min ago i took a wire and jumped r and y together at the unit and the contactor engaged but when i pulled the jumper it disengaged


any help would be appreciated
thanks
 
  #2  
Old 11-08-04, 09:19 AM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

Id start at the tstat first and see if R to Y there will pull it in If so can be the tstat if not then look at the wires.
For heat R -power Y -compressor G -fan and you can have O or B for the changeover valve or called the 4 way valve. You see you need all of them for heat. What works when you put it on cool??

 
  #3  
Old 11-09-04, 03:45 PM
hvac4u's Avatar
Member
Join Date: Aug 2001
Location: NW atlanta
Posts: 3,049
Upvotes: 0
Received 0 Upvotes on 0 Posts
tells us there is no call from inside on Y, could be stat, possibly, sounds like you need a pro unless you are comfortale with and have a volt meter
 
  #4  
Old 11-10-04, 09:55 AM
bob1968
Visiting Guest
Posts: n/a
ok i jumped the r and y at the tstat and still nothing at the outside unit......and yes i have a volt meter and use it quite often in my line of work.....i drill and service water wells for a living.....from household use all the way to city usage....so i am familiar with electricity


thanks
bob
 
  #5  
Old 11-10-04, 09:56 AM
bob1968
Visiting Guest
Posts: n/a
oh and the outside unit dont come on with the cool either
 
  #6  
Old 11-10-04, 04:57 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

With the volt meter see if you have 24 Volts out there at the contactor When you have tstat on heat or cool and call for it. Can be its coil check this out next
.

ED
 
  #7  
Old 11-10-04, 06:02 PM
heatpumpman
Visiting Guest
Posts: n/a
Check your low and/or high pressure switches...

at the outside unit. Trace the yellow wire into the unit and all the way to the contactor.
 

Last edited by heatpumpman; 11-10-04 at 06:05 PM. Reason: Didn't read post entirely
  #8  
Old 11-12-04, 05:17 PM
hvac4u's Avatar
Member
Join Date: Aug 2001
Location: NW atlanta
Posts: 3,049
Upvotes: 0
Received 0 Upvotes on 0 Posts
there is a high pressure manual reset in that unit,

TURN POWER OFF FIRST

there was a problem with that switch's location as i recall, your installer should have the TM addemdum

good call heatpumpman
 
  #9  
Old 11-21-04, 09:12 AM
bob1968
Visiting Guest
Posts: n/a
man i feel like a complete fool........first i want to thank all of you for your advice and help.......i traced the yellow wire to the reset button....darn near need to take the whole unit apart to get to the reset button....i pushed it and voila it now works.....i have been using emergency heat for 3 weeks because of a 10cent reset....

thanks

ps. is there a reason or fault that the reset needed to be reset
 
  #10  
Old 11-21-04, 09:19 AM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

Could be high head---- but why???? fan not come on dirty coil out side or inside. filter clean?????


ED
 
  #11  
Old 11-21-04, 10:21 AM
hvac4u's Avatar
Member
Join Date: Aug 2001
Location: NW atlanta
Posts: 3,049
Upvotes: 0
Received 0 Upvotes on 0 Posts
as i recall the position of the switch was faulty, causing nuisance trips


but then again be sure the coil is clean and the fan spins freely
 
 