heat pump question

Reply

  #1  
Old 01-12-05, 08:55 PM
milesfrmhm
Visiting Guest
Posts: n/a
heat pump question

I have a Rheem w/scroll heat pump that will not stop running unless I turn off the circuit breaker. The weather was about 60 today and the air was off all day. The crazy thing still ran and froze up all copper inside, the compressor, and a long skinny cylinder which on a car I would assume was an evaporator. The h/p makes cold and warm air. It just won’t shut off. Any hint to a solution would be great. JM
 
  #2  
Old 01-12-05, 09:10 PM
mattison's Avatar
Member
Join Date: Mar 2003
Location: Cinti, OH
Posts: 5,548
Received 0 Votes on 0 Posts
The contactor in the outdoor unit is probably stuck closed. Do you have a volt tester?
 
  #3  
Old 01-12-05, 09:16 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Remove the t-stat from the subase on the wall. If it stops, then it's the t-stat.. but if keeps on running. Check the wire going outside to make sure there is no short.

If you don't have a meter, remove the low voltage wire that feeds the contactor. if it still runs, then the contactor needs to be replaced.

If it stops when you remove, then you need to look at the t-stat wire for a short or in the furnace.
 
  #4  
Old 01-13-05, 03:37 PM
milesfrmhm
Visiting Guest
Posts: n/a
Thumbs up

I really apreciate the help, yall were right on the money with the contactor in the outdoor unit.
 
  #5  
Old 01-13-05, 08:43 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Thanks for the update!

Did you replace it yourself or had a service co come in?
 
 