Do programmable thermostats need an isolation reley?
#1
Do programmable thermostats need an isolation reley?

Hello I am new to this.
I purchased and installed a Hunter programmable thermostat [Auto Saver #44550] to go with My Lenox High Efficent gas furnance. Long story short after installing the thermostat it did damage to the tune of $700.00. [Damaged my ignation control and my gas value] My furnace company said I needed an isolation reley before I installed the thermostat and hope that it did not do any damage. A little to late for that idea.
Hunter fan company which produced the thermostat said it was not their fault. But the furnace company they always put a isolation reley with a programmable thermostat.
How would I know to install an isolation reley?
After the fact the people at Lowes and a True Value Hardware did not know this.
Is this correct? Help!
Thanks!
TodLee
#2
I have never heard of this.
I think you had a wired crossed or wrong, and shorted out the controls. or didn't turn of the power when you wired the new stat.
This furnace a single stage or two stage?
If they put in a relay, how does the stat get it's power??
I think you had a wired crossed or wrong, and shorted out the controls. or didn't turn of the power when you wired the new stat.
This furnace a single stage or two stage?
If they put in a relay, how does the stat get it's power??
#3
Hi Jay11J,
Before I started I had a frenid with me and we made sure the power was off.
I am 99.99999% sure we did not cross any wires because the week before he had installed a Hunter programmable thermostat himself and he has more experience than me.
The furnance was working but erraticlly.
The last time I tried I took the thermostat to Lowes and they said to [check if it is the furnance or the thermostat] by over riding the thermostat by toching two wires together with the thermostat off of the wall. Before attempting, I called Hunter and with them on the phone and the thermostat off the wall I touched two wires together with the power on to the furnance and got nothing. That's when Hunter said it was the furnace.
I even called Lenox who manufactured the furnace with the model# and serial# and they said the same thing "WE ALWAYS INSTALL A ISOLATION RELEY WITH A PROGRAMMABLE THERMOSTAT'' I asked can you show me or tell how I can verify this? He said only if I was a certified thec. working for a company. He however said I can use him as a witness.
How can I tell if mine is a single or two stage furnace w/out calling someone.
Thank you for the reply.
TodLee
Before I started I had a frenid with me and we made sure the power was off.
I am 99.99999% sure we did not cross any wires because the week before he had installed a Hunter programmable thermostat himself and he has more experience than me.
The furnance was working but erraticlly.
The last time I tried I took the thermostat to Lowes and they said to [check if it is the furnance or the thermostat] by over riding the thermostat by toching two wires together with the thermostat off of the wall. Before attempting, I called Hunter and with them on the phone and the thermostat off the wall I touched two wires together with the power on to the furnance and got nothing. That's when Hunter said it was the furnace.
I even called Lenox who manufactured the furnace with the model# and serial# and they said the same thing "WE ALWAYS INSTALL A ISOLATION RELEY WITH A PROGRAMMABLE THERMOSTAT'' I asked can you show me or tell how I can verify this? He said only if I was a certified thec. working for a company. He however said I can use him as a witness.
How can I tell if mine is a single or two stage furnace w/out calling someone.
Thank you for the reply.
TodLee
#4
Member
Join Date: Dec 2005
Posts: 179
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Originally Posted by TodLee

Hello I am new to this.
I purchased and installed a Hunter programmable thermostat [Auto Saver #44550] to go with My Lenox High Efficent gas furnance. Long story short after installing the thermostat it did damage to the tune of $700.00. [Damaged my ignation control and my gas value] My furnace company said I needed an isolation reley before I installed the thermostat and hope that it did not do any damage. A little to late for that idea.
Hunter fan company which produced the thermostat said it was not their fault. But the furnace company they always put a isolation reley with a programmable thermostat.
How would I know to install an isolation reley?
After the fact the people at Lowes and a True Value Hardware did not know this.
Is this correct? Help!
Thanks!
TodLee
TodLee,
I once had to install an isolation relay on a Lenox system to control the cooling mode. Once I started investigating the problem I realized the t/stat would drop just enough voltage to the "cool" wire to cause the contactor to drop out. I installed the relay (one of the ice cube types) and wired as so (AFTER all power is removed from the system....make sure the 24v side is dead also):
"Cool" wire from t/stat to coil side of relay (normally #85 or 86 terminal)
Ground the other side of the coil
Hot wire (24v) to terminal #30
24v "cool" wire to compressor to #87a (N/open)
I don't see any reason the same wiring wouldn't work with the heat mode. A word of caution though....I think most gas valves work on approx 3.5 volts so the relay would have to feed the gas valve the correct voltage....NOT 24v!
Hope this helps.
#5
That is still new to me about this relay.
I just put in a Honeywell Vision Pro on my supervisor's furnace. and he has the Lennox G61v.
I must say, I do hear alot of horror stories on these off hand t-stat like Hunter. I have not seen it for myself tho..
I just put in a Honeywell Vision Pro on my supervisor's furnace. and he has the Lennox G61v.
I must say, I do hear alot of horror stories on these off hand t-stat like Hunter. I have not seen it for myself tho..
#6
Member
Join Date: Dec 2005
Posts: 179
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I agree with you about the Hunter t/stat....never experienced any problems installing/using Honeywell. A quick voltage check at the t/stat will reveal if the heat mode is being signaled and the same check at the gas valve. I'd bet the t/stat supplied 24v to the gas valve/related controls causing the damage, thus the reason for the isolation relay.
#7
Thanks for the information.
I can't belive I am the only that has had this problem.
I asked this same question to www.AskTheBuilder.com {Tim Carter Cincinnati, Ohio} "He tells people NOT to install thoses things themselves....
The electrical components in a modern furnace are VERY sophisticated."
I did not know Hunter thermostats have had some horror stories.
I feel Hunter has some obligation to notify the consumer about installing thermostats on modern furnaces. I guess the next move is to small claims court.
I can't belive I am the only that has had this problem.
I asked this same question to www.AskTheBuilder.com {Tim Carter Cincinnati, Ohio} "He tells people NOT to install thoses things themselves....
The electrical components in a modern furnace are VERY sophisticated."
I did not know Hunter thermostats have had some horror stories.
I feel Hunter has some obligation to notify the consumer about installing thermostats on modern furnaces. I guess the next move is to small claims court.