I have bad duct board and need to replace with flex or other material. I have the standard 4" x 10" registers and could easily change flanges to the duct type, but I'm not sure how to size the ducting to ensure that I can maintain the static pressure required for my a/c unit. The cross over duct is 12" flex and provides adequate supply to the trunk line so is 12" for front and 12" for rear the way to go then down size at some point?
Also, if registers are 40 sq. " then should I strive to have 8" duct to registers or 6"?
 
  #2  
Old 07-12-06, 05:14 AM
M
Forum Topic Moderator
Join Date: Mar 2005
Location: USA - N.E.Tn
Posts: 45,659
Received 835 Upvotes on 732 Posts
I'm moving your post to the heating section where you will be better served.
 
  #3  
Old 07-12-06, 10:39 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

You dont say what you have there as to size of the AC or heat. Ill try this .you should have 400cfm per ton Like a 3 ton will have 1200 cfm now off the trunk line or what . 10" pipe is 400cfm now you can take 2-- 8 " pipes out of the 10" then 2 6" out of each 8". So now you have 4 6" runs at a 100cfm that can go to 4 4X10" registers.

ED
 
  #4  
Old 07-13-06, 10:03 AM
W
Member
Thread Starter
Join Date: Jul 2006
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ed,

I also have a thread that has specific information if you don't mind taking alook and thanks for your reply! You should be able to find the thread under my posts.
 
 

Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: