Ducane 3T HP Issues

Well let me start from the beginning I've had the hvac company out here twice and now for a third time for a problem that keeps occuring and now seems to have changed.

Last thursday they came out because my low pressure switch was open. I check the states of the switches before I called them out and the low read open. When they got out here they found a pin hole leak in one of the 1/8 lines that feeds the coils in the fins on the outdoor unit. The tech said the lines weren't spaced right at the factory and two were rubbing together for the last two years since the unit was installed. He repaired the line by just soldering it, it looked like. He then purged the system and recharged the line, he checked for a leak with a micron gauge. The system temps coming out of the vents were fine and flow was fine, he left. I came home from work thursday and the system was not working again, and the low pressure switch was open again. I called them on friday and they couldn't get a tech to me til monday morning.

Monday, the same tech came out, and appologized that his repair didn't hold, the leak was in the same place. He patched again, looked the same to me, and repeated the same process. It ran for 24 hours and now its doing something thats baffling me.

I have it in cool mode, the out door unit turns on for roughly 30 seconds and cuts out. The low pressure switch and the high pressure switch are in closed states. If I put my meter on the 24vac coil on the contactor when the unit turns on it gets 24vac to the side of the contactor and starts, 30 seconds later it loses power to the contactor and shuts off. I still read 24vac when I meter from the Red power wire to the Yellow stage 1 cooling wire that should energize the contactor. Are there any other steps that can prevent the unit from turning on other than the high and low pressure switches? And does anyone have a clue as to whats going on. I've been run through the ringer already and fought to have the second bill wiped, I'd like to be armed with some info when they come back. Thanks in advance.
 
Sponsored Links
  #2  
Old 04-24-07, 07:39 PM
Member
Thread Starter
Join Date: Nov 2005
Location: Somewhere, USA
Posts: 80
Received 0 Votes on 0 Posts
Ran another test myself. I stuck my meter on the low pressure switch, and then gave it a demand to cool, before the unit turned on the switch read closed, signifying the pressure was within parameters. When the unit turn on after 5 seconds the switch went open and stayed open, the unit shut down and then it closed after about 2 mins.

Any ideas of what technically going on?
 
  #3  
Old 04-28-07, 08:12 PM
Member
Join Date: Mar 2007
Posts: 76
Received 0 Votes on 0 Posts
refrigerant shortage

Yes, what's happening is the low pressure control is responding to the low side refrigerant pressure in the system and cycling the unit on/off. When the compressor is running it is pumping refrigerant from the low side of the system to the high side. If there is a shortage of refrigerant, the low side pressure will keep going down because not enough refrigerant is coming back to low side from the high side to keep up with the pumping capacity of the compressor. The low pressure switch is there to keep the compressor from running in case all the refrigerant leaks out. Running the compressor with no or very little refrigerant in the system will destroy it. My first thought is the leak is still not repaired properly. Soldering is not the way to repair the leak, it should be brazed. If the tech is just trying to cover the leak with soldering material it won't work. I suggest that he make a sleeve from some 1/4" copper tubing, cut the leaking tubing, slide the ends into each end of the sleeve, crimp the sleeve at the ends but not so much as to crimp the smaller tubing shut; then braze the ends of the sleeve shut. BTW- no way did he pass a micron guage test to prove that his repair was good. Use of a micron guage is part of the evacuation/dehydration process.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: