3 Ton Heat Pump-2 1/2 Air Handler

ICP replaced my 2 1/2 heat pump. When the new unit got there is was a 3 ton. I was told that it would not work correctly by someones else because of having a 2 1/2 ton air handler.

I thought that Heil's air handlers were only single diget, such as 2, 3, 4, or 5 and no halves. Is this correct? Also I have no espansion valves. Does that matter?
 
  #2  
Old 06-10-07, 09:50 AM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,386
Received 1 Vote on 1 Post
Wink

I for sure would not put a 3 ton high side on a 2 1/2 blower coil. Coils work ok with a orifice or a capillary tube or better with a TXV valve on them.
 
 