Honeywell Thermostat

Electric Furnace
Central Air

Old thermostat was a honeywell and the new is a honeywell RTH230B. Everything matches up for the wiring except that the old thermostat has a W1 and a W2. The new thermostat only has a W. Any insight to this would greatly be appreciated.

Thanks!
 
  #2  
Old 06-18-07, 12:16 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 37 Likes on 29 Posts
The old thermostat has a two-stage heating system. If you have only one "W" wire you would connect it to the "W" terminal on the new thermostat.

If you have two "W" (W1 & W2) wires then you need a different thermostat. The one with only a "W" terminal is a single-stage heating thermostat.
 
 