Ruud Acheiver - Fan and Compressor not starting

I have a Ruud Acheiver Heat Pump. When I lower the Temp on the Thermostat, there is no cool air. The Indoor fan works, however, the Compressor and the Outdoor fan do not work.

I verified the thermostat triggers the compressor switch. I also hear faint buzzing noise (coming from the compressor switch, I believe) however the fan and the compressor do not start up. The fan is not stuck.

As I understand it, there should always be 220V to the compressor switch lead. This is true when the compressor switch is NOT engaged. However, when I turn on the A/C from the Thermostat, and the compressor switch is engaged, I no longer have power at the compressor switch lead.

I spoke with a Parts supplier and he said it didn't sound like a problem with the switch but rather an electrical problem. Does that sound accurate? Is there anything that could happen to the Heat Pump that would cause the Electrical source to drop at the compressor switch lead or does in fact sound like an electrical issue?
 
Sponsored Links
  #2  
Old 07-25-07, 11:55 AM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,386
Received 0 Votes on 0 Posts
Wink

If you mean the 24V could be the defrost board. If you push the contactor in will the compressor run ?? So do you have 24V at the contactor?? does it pull in?? Do you have 220V on the line from it to the compressor???
 
  #3  
Old 07-25-07, 08:01 PM
C
Member
Join Date: Mar 2007
Location: Jacksonville
Posts: 157
Received 0 Votes on 0 Posts
you may want to call a service company.
If you are not familiar with electrical components it's best to call someone who is.
 
  #4  
Old 07-29-07, 11:12 AM
S
Member
Thread Starter
Join Date: Jul 2007
Posts: 5
Received 0 Votes on 0 Posts
Sorry for the delay in getting back to you on your reply...

I do have 24V at the Contactor. The thermostat does trigger the contactor on/off if that's what you mean by "pull in"...Also, if I push the contactor in, the compressor and fan do NOT run. I have no voltage going to the compressor or the fan.


Originally Posted by Ed Imeduc View Post
If you mean the 24V could be the defrost board. If you push the contactor in will the compressor run ?? So do you have 24V at the contactor?? does it pull in?? Do you have 220V on the line from it to the compressor???
 
  #5  
Old 07-31-07, 12:52 PM
C
Member
Join Date: Dec 2006
Posts: 8
Received 0 Votes on 0 Posts
Check the control board

Since neither the fan nor the compressor work, check the dual capacitor.

You state that you have 230V coming to the contactor, but it does not make it to the compressor. Is this correct?

There may be a reset switch on the compressor, but if that were the case
your condenser fan would still work.
 
  #6  
Old 07-31-07, 07:38 PM
S
Member
Thread Starter
Join Date: Jul 2007
Posts: 5
Received 0 Votes on 0 Posts
I do have 244 V going to the contactor. There is no Voltage going to the compressor and the reset switch on the compressor didn't help. I will check the dual capacitor...


Originally Posted by cubswin1 View Post
Since neither the fan nor the compressor work, check the dual capacitor.

You state that you have 230V coming to the contactor, but it does not make it to the compressor. Is this correct?

There may be a reset switch on the compressor, but if that were the case
your condenser fan would still work.
 
  #7  
Old 08-01-07, 10:29 AM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,386
Received 0 Votes on 0 Posts
Wink

Do you have 220V comeing off the contactor????? Could have bad points on it.
 
  #8  
Old 08-01-07, 05:56 PM
S
Member
Thread Starter
Join Date: Jul 2007
Posts: 5
Received 0 Votes on 0 Posts
I have replaced the contactor with an identical one from my other RUUD Heat Pump...same result. there is not 220V coming off the contactor...
 
  #9  
Old 08-05-07, 12:25 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,386
Received 0 Votes on 0 Posts
Wink

Do you have 220V to the in --side of the contacror??????
 
  #10  
Old 08-21-07, 09:49 PM
S
Member
Thread Starter
Join Date: Jul 2007
Posts: 5
Received 0 Votes on 0 Posts
The problem was the cut-off switch and not the Heat Pump.

The contacts were bad and after I replaced that I didn't have any problems.

Scott
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: