air handler blues
#1
Member
Thread Starter
Join Date: Nov 2006
Location: nc
Posts: 57
Likes: 0
Received 0 Likes
on
0 Posts

I have noticed that intermittantly, the air handler skips an "on" cycle, when the outside unit kicks on. My fix for this has been to set the tstat control from "cool" to "off" and then to "heat" then back to "off".I turned the fan switch from "auto" to "on", to see if the fan would come on and it does. wait a few minutes and turn it back to "cool", after a short delay it comes on. Fan motor is good, thermostat control is good, capacitor is good. I don't have a system drawing to see what parts wire in the line

#2
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,386
Likes: 0
Received 1 Like
on
1 Post

Check blower relay or the blower control board. Sounds like you can have a time delay on that blower control board . The G wire should go to it in the blower unit.
Can jump R to G at tstat should get fan if you dont after a short time can be fan control in the tstat .
Can jump R to G at tstat should get fan if you dont after a short time can be fan control in the tstat .
#3
Member
Thread Starter
Join Date: Nov 2006
Location: nc
Posts: 57
Likes: 0
Received 0 Likes
on
0 Posts
I installed a new thermostat control when it started this but didn't fix it. Where would the blower relay or the blower control board. be at ?
The fan work fine if you go"cool" to "off" and then to "heat" then back to "off " then "cool"
.


#12
Member
Join Date: Oct 2005
Location: USA
Posts: 1,076
Likes: 0
Received 0 Likes
on
0 Posts
That pretty much nails it down. Your relay is bad. On newer units the relay is on a circuit board. In this case, you replace the board. Its easy to find, the motor wires connect to it.
It's not unusual to have a relay fail intermittently. This can be a little frustrating. It may work perfectly 100 times in a row, then when no one is watching, it doesn't work.
It's not unusual to have a relay fail intermittently. This can be a little frustrating. It may work perfectly 100 times in a row, then when no one is watching, it doesn't work.
#13
Member
Thread Starter
Join Date: Nov 2006
Location: nc
Posts: 57
Likes: 0
Received 0 Likes
on
0 Posts



#15
Member
Join Date: Aug 2007
Posts: 2,021
Likes: 0
Received 0 Likes
on
0 Posts



there still has to be a relay to run the indoor fan on a call for cooling, it's probably wired in parallel to the sequuncer trace the wires back from the fan motor to find it the problem as you describe it would involve the defrost board.
#17
Member
Thread Starter
Join Date: Nov 2006
Location: nc
Posts: 57
Likes: 0
Received 0 Likes
on
0 Posts
COULD MY DEFROST COTROL CIRCUIT BOARD IN MY OUTDOOR UNIT HAVE SOMETHING TO DO WITH THIS I THINK THAT IT MAY NOT BE DEFROSTING RIGHT? IF NOT I LOOK IN THE AIR HANDLER NO CIRCUIT BOARD RELAY IN THERE. I SEE WHAT LOOKS LIKE TO FAN COIL SEQUENCER BLOWER CONTROL TIME DELAY RELAY ONE HAS WIRE LEADS FROM FAN GOING TO IT. THE OTHER LOOKS LIKE IT GOES TO HEAT STRIPS. WHAT DO YOU THINK
the interior fan cut out on heat or cool
the interior fan cut out on heat or cool
#18
Member
Thread Starter
Join Date: Nov 2006
Location: nc
Posts: 57
Likes: 0
Received 0 Likes
on
0 Posts
COULD MY DEFROST COTROL CIRCUIT BOARD IN MY OUTDOOR UNIT HAVE SOMETHING TO DO WITH THIS I THINK THAT IT MAY NOT BE DEFROSTING RIGHT? IF NOT I LOOK IN THE AIR HANDLER NO CIRCUIT BOARD RELAY IN THERE. I SEE WHAT LOOKS LIKE TO FAN COIL SEQUENCER BLOWER CONTROL TIME DELAY RELAY ONE HAS WIRE LEADS FROM FAN GOING TO IT. THE OTHER LOOKS LIKE IT GOES TO HEAT STRIPS. WHAT DO YOU THINK
the interior fan cut out on heat or cool
the interior fan cut out on heat or cool
#19
Member
Thread Starter
Join Date: Nov 2006
Location: nc
Posts: 57
Likes: 0
Received 0 Likes
on
0 Posts

OK I Have replaced both DELAY RELAY inside air handler and capacitor on motor also thermostat
it work fine after replacement of parts for 5 days and its right back to the air handler skips an "on" cycle, when the outside unit kicks on the blower don't about every other day or so
.


#20
Member
Join Date: Oct 2005
Location: USA
Posts: 1,076
Likes: 0
Received 0 Likes
on
0 Posts
Hmmmmm. On some units, the defrost board may control the indoor blower at certain times. Such systems use a low pressure switch to initiate the defrost cycle rather than a timer.
This type of setup can be a little tricky to diagnose.
This type of setup can be a little tricky to diagnose.
#22
Member
Join Date: Aug 2007
Posts: 2,021
Likes: 0
Received 0 Likes
on
0 Posts
just because the delay relay is new don't assume it's a good one.
#26
Member
Join Date: Oct 2005
Location: USA
Posts: 1,076
Likes: 0
Received 0 Likes
on
0 Posts
I've done that a few times too. Those Goodman time delay relays can have a short life and often fail intermittently. I have seen them go bad in less than 2 years.
Perhaps the wrong relay was replaced. The blower td relay looks like an electric heat stack relay with 5 connections. 2 for the 24 coil and 3 others labeled 1,2 and 3.
Post some pics if possible.
Perhaps the wrong relay was replaced. The blower td relay looks like an electric heat stack relay with 5 connections. 2 for the 24 coil and 3 others labeled 1,2 and 3.
Post some pics if possible.