Heat pump wont stop but no air from ducts
#1
Member
Thread Starter
Join Date: Jan 2008
Posts: 5
Received 0 Votes
on
0 Posts
Heat pump wont stop but no air from ducts
My Bryant heat pump won't stop running. When I turn on the thermostat, the heat pump runs but the air doesn't come out. When I turn on the emergency heat, hot air comes out then. I went out to the unit and pulled the fuse box and when it stopped running, it made this hissing sound for a couple of minutes. There is no frost on the unit. I had problems with the air handler last month. I replaced the 5 amp fuse. Turned out that there was a wire inside the heat pump that had rubbed up against the copper tubing and was shorting the system. Any suggestions on how to fix this thing. Any suggestions would be greatly appreciated.
#2

Does it run when the tstat dont call for heat like you push it all the way down??? Does the blower come on when you go to fan on??? Units can hiss at you when they go off.
#3
Member
Thread Starter
Join Date: Jan 2008
Posts: 5
Received 0 Votes
on
0 Posts
Response
It doesn't run when the tstat doesn't call for it. The blower didn't come on when I put the fan on. When I called for the heat, the heat pump does run but no air comes out. I put it back on emergency heat, it heats the house. Something in the heat pump? Thanks again!
#4

The blower didn't come on when I put the fan on. When I called for the heat, the heat pump does run but no air comes out.
#5
Member
Join Date: Jan 2008
Posts: 9
Received 0 Votes
on
0 Posts
I had a similar problem. It turned out that the contactor in the outside unit was bad. It was staying closed, that is, the unit was being powered even when the t-stat was NOT calling for it. Hence, the outside unit stayed on all the time. I changed the contactor and my heat pump has been working fine.
The fact that you mention that the heat pump keeps running while there is no air through the vents, leads me to believe that the t-stat is calling for the whole system to stop running. The indoor unit is working correctly and hence there is no air through the vents. However, the outdoor unit is not working correctly and the contactor may be a problem.
The fact that you mention that the heat pump keeps running while there is no air through the vents, leads me to believe that the t-stat is calling for the whole system to stop running. The indoor unit is working correctly and hence there is no air through the vents. However, the outdoor unit is not working correctly and the contactor may be a problem.