Heat Pump (?) Problems

Forgive my stupidity, but really need some advice. I have a GE unit with a heat pump. The heat or a/c will not turn on, although the fan will.

A couple of days ago, we had an electrical outage for a few hours. I checked the circuit breaker and all seemed well. Is there anything else I need to check?

Thanks in advance for any advice.
 
  #2  
Old 03-06-08, 10:28 AM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,386
Received 0 Votes on 0 Posts
Wink

Need to find out where and if you have power to the inside and outside units first. You say the inside fan will run. So I take it you have 220V inside and 24V there. So check the outdoor unit for 220V inside it and if the 24V go to the contactor when calling for heat or cool.
 
  #3  
Old 03-06-08, 02:35 PM
M
Member
Thread Starter
Join Date: Mar 2008
Posts: 2
Received 0 Votes on 0 Posts
Problem Resolved

Seemed to be one of those fluke things. Turned the breaker off; then on. Replaced the batteries and reset the thermostat. Thanks for the kind input!
 
 