air handler blower wont cut off!!!!!!! help!!!!
#1
Member
Thread Starter
Join Date: Dec 2008
Location: richmond, virginia
Posts: 2
Received 0 Votes
on
0 Posts

here we go. i have a air handler in the upstairs of our home. it worked fine after i installed a new digital thermostat. one day we apparantly got hit by lightning. a few ceiling fans and the heat pump air handler stopped working. repaired ( replaced ceiling fan) when i opened the air handler their were some burnt wires on what i assume is the blower relay. repaired the wires and replaced the relay. blower seemed to work fine. all the sudden the blower will ot turn off. switch is off anf fan is on auto. also removed thermostat and left sub base hooked up , still stays on. here is a list of my thermostat and unit model numbers. can anyone help. this is a problem for the bill when it just runs 24 - 7 even if the heat or ac is off the blower runs. maybe i hooke a wire back up wrong?
thermostat: honeywell ct3611r 44503
0339e
sub base honeywell: 32207415-056
0333
has six wires r = red wire
w2= white
e= brown
y= yellow
o= gray
g= green
outside heat pump: gmc model # cple-24-1
serial # 0203469489
inside air handler: gmc model# ar24-1
serial# 0203522278
any help is appreciatted.
thanks.

art divittorio
thermostat: honeywell ct3611r 44503
0339e
sub base honeywell: 32207415-056
0333
has six wires r = red wire
w2= white
e= brown
y= yellow
o= gray
g= green
outside heat pump: gmc model # cple-24-1
serial # 0203469489
inside air handler: gmc model# ar24-1
serial# 0203522278
any help is appreciatted.
thanks.


#2
Member
Join Date: Jan 2008
Posts: 49
Received 0 Votes
on
0 Posts
Sorry to hear about the lightning strike. You can't trust anything after a lightning strike.
I'd start by disconnecting all the tstat wires from the air handler. Does this stop the blower? If so get a multimeter and see if any of the tstat wires are shorted/melted together somewhere from the lightning strike. If the wires are connected to nothing at the tstat end and nothing at the air handler you should have infinite resistance between any two wires. If any combination reads anything even close to 0 replace the wire, its internally melted somewhere.
-Doug
I'd start by disconnecting all the tstat wires from the air handler. Does this stop the blower? If so get a multimeter and see if any of the tstat wires are shorted/melted together somewhere from the lightning strike. If the wires are connected to nothing at the tstat end and nothing at the air handler you should have infinite resistance between any two wires. If any combination reads anything even close to 0 replace the wire, its internally melted somewhere.
-Doug