10kW, 15kW, or 20kW Heater?
Old 03-24-09, 02:54 PM
Received 22 Votes on 17 Posts
I need to know what size heater coil to purchase with my new air handler. Two story house with finished basement (3 levels total), 2200 sq. feet.
Old 03-24-09, 05:42 PM
airman.1994's Avatar
Received 8 Votes on 8 Posts
You will have to do a heat load to know!
Old 04-18-09, 03:55 PM
I
If this is your only source of heat then go with 20kw (or even 25kw if available). The heaters typically come in pieces of 5 kw, so that for 20kw you get four 5kw heaters.
So if you buy too large, you can always switch one or more of the 5kw elements off.
If this is backup heat for a furnace or heat pump then size the electric heater to be roughly the same as the primary heat source.
For example, if you have a 3 ton heat pump, that means that at 47F it will put out 3*12000 = 36000 btu/hr. Each 1kw is equivalent to 3412 btu/hr, so 10kw is 34120 btu/hr - so that'd work - but go a little larger won't hurt.
The only reason not to go with larger electric heat (not much extra expense) is that the electrical wiring from the main breaker box to the air handler has to be sized to the load - so the wiring could be more expensive.