Trane Heat Pump Weatertron Stat

I have a Trane weathertron thermostat with 8 wires, R,C,O,W,B,G,Y & T . How do you wire this up to a Honeywell RTH7500D the insructions do not list a T wire anywhere ?
 
  #2  
Old 05-07-09, 08:38 PM
Z
Member
Join Date: Sep 2006
Location: Connecticut
Posts: 242
Received 2 Upvotes on 1 Post
old new
--- ---
R R and jumper to RC
C C
O O/B
W AUX
G G
Y Y

T is not used on the Honeywell as it is for compressor lockout.
 
  #3  
Old 05-08-09, 03:12 PM
Jarredsdad's Avatar
Member
Join Date: Oct 2002
Location: Troy, VA
Posts: 1,392
Upvotes: 0
Received 0 Upvotes on 0 Posts
As said.

T is not needed even if you put in a new weathertron.
 
 