York 7 Wire to Honeywell 7600D

Trying to replace my current York T-stat (not sure of model #) with the Digital Programmable Honeywell RTH7600D for Heat Pumps.
Old Wiring on York:
W-white
B-blue
G-green
R-red
X-black
O-orange
Y-yellow

Hooked up the Honeywell as follows:
R-RC with jumper to R
O-O/B
Y-Y
G-G
B-C
X-E
W-Aux

[IMG][/IMG]

When AC is turned on - compressor outside works great.
When Heat is turned on - compressor does not turn on. Waited over 10min.
 
  #2  
Old 10-23-09, 10:46 AM
dun11's Avatar
Member
Join Date: Feb 2009
Location: Local
Posts: 753
Upvotes: 0
Received 1 Upvote on 1 Post
Did you go into the installer set up and configure the stat for a heat pump?
 
  #3  
Old 10-23-09, 05:21 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
As Dun pointed out, sounds like you don't have the t-stat set up correct in the set up menu.


Go to page 13, and follow how to get in to the Menu.

These are the settings I suggest.

170-7
180- I don't know what you got, set up to what you have for back up heat.
190-0
240-3
270-3

Rest you can figure out, ask if you have any questions.
 
 