Crankcase Heater controls

Hello people. I am having a fit with my Nordyne supplier on a crankcase heater for a 5 ton dual fuel package unit. Nordyne does not have a control tstat for the crankcase heater so it wires directly to L1 and L2 and runs all the dang time. From the information I have gathered that adds about 6 dollars per month to my electric bill. Apparently Trane Carrier and possibly some others use a compressor discharge line tstat that simply wires into the CCH wiring so it only comes on when needed (when the compressor discharge line is below 65F) which makes way more sense to me. Can some of you dudes get me some information and a part number so I can order me up one and DIY please.
 
  #2  
Old 01-22-10, 02:42 PM
Jarredsdad's Avatar
Member
Join Date: Oct 2002
Location: Troy, VA
Posts: 1,392
Upvotes: 0
Received 0 Upvotes on 0 Posts
A lot of Carrier and Trane units I've seen wire through L1 and T1 of a single pole contactor so that the heater only works when the compressor is off, contactor open.

When I contacter Bristol about the scroll in my Luxaire heat pump because the check valve stuck open periodically allowing the comp to run in reverse when it shut down the guy I talked to asked about a heater. He recommended one, and I didn't have one.

When I added an extrernal check valve I also installed a wrap around heater to the compressor. Since I have a 2 pole contactor I added a relay to power the heater when the compressor contactor is off. So contactor energized heater off, contactor de-energized heater on.

You could certainly modify this by using a close on fall temp switch breaking "R" to a relay at 65 degrees if you can find the temp switch. Klixon must have something. But how often are defrost problems a faulty temp switch?
 
  #3  
Old 01-22-10, 02:46 PM
Jarredsdad's Avatar
Member
Join Date: Oct 2002
Location: Troy, VA
Posts: 1,392
Upvotes: 0
Received 0 Upvotes on 0 Posts
If you can post a Trane or Carrier model number with the control you mentioned I can try and chase it down and find part number and maybe the original manufacturer.
 
  #4  
Old 01-22-10, 04:53 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,475
Received 89 Upvotes on 82 Posts
Trane had this discharge line thermostat in their units...



 
  #5  
Old 01-23-10, 12:44 PM
Jarredsdad's Avatar
Member
Join Date: Oct 2002
Location: Troy, VA
Posts: 1,392
Upvotes: 0
Received 0 Upvotes on 0 Posts
Trane part number THT00811 $25
THERMOSTAT, TERMINATOR, 240V (SETTING OPEN @ 105 DEGREE F, CLOSE @ 73 DEGREE F), FOR CLIP USE CLP00185.

The clip is $1.08
 
  #6  
Old 01-30-10, 04:18 PM
Former Member's Avatar
Member
Thread Starter
Join Date: May 2006
Location: US
Posts: 726
Upvotes: 0
Received 0 Upvotes on 0 Posts
hey dad just wanted to thank you for taking the time to hunt down those part numbers for me. That is exactly what I needed worked like a charm. Payback is estimated at 4 months, cannot beat that with a stick.
 
  #7  
Old 01-30-10, 04:22 PM
Jarredsdad's Avatar
Member
Join Date: Oct 2002
Location: Troy, VA
Posts: 1,392
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hey, no problem brother. Just a click here and a click there.

Beer 4U2
 
  #8  
Old 02-24-10, 03:52 PM
R
Member
Join Date: Feb 2010
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Down Side

So what's the downside of not having the crankcase heater operational. I live in a cold climate and I cannot think of a single reason to have this heater operational during the cold months. And certainly would like to save the $6-$10/mo elec charge if it's not necessary. Can I just trip the cb and call it good?
 
  #9  
Old 02-24-10, 10:49 PM
braether3's Avatar
Member
Join Date: Nov 2009
Location: wisconsin
Posts: 387
Upvotes: 0
Received 0 Upvotes on 0 Posts
it keeps liquid refrigerant out of the compressor ...you can shut it off but must turn it back on well before you turn on the unit
 
  #10  
Old 02-25-10, 02:40 PM
Jarredsdad's Avatar
Member
Join Date: Oct 2002
Location: Troy, VA
Posts: 1,392
Upvotes: 0
Received 0 Upvotes on 0 Posts
And you should turn it back on AT LEAST 24 hours before you start the unit. If not, all the money saved keeping it off will pay 1% of the new comrpessor you will need.
 
  #11  
Old 02-26-10, 02:06 PM
R
Member
Join Date: Feb 2010
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks Guys. I'll keep all this in mind.
 
 