My American Standard Air handler won't turn off


  #1  
Old 10-11-11, 09:18 AM
J
Member
Thread Starter
Join Date: Oct 2011
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
My American Standard Air handler won't turn off

I have an American Standard Air handler off of a Trane Heat pump that will not turn off the model number is twh736b140a0. I'm thinking maybe a relay is bad, anyone know of a solution or replacement part. Thank You.
 
  #2  
Old 10-11-11, 02:35 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,244
Received 4 Votes on 4 Posts
by not shutting off do you mean that the fan continues to run? Is the thermostat fan switch on ON or AUTO?
 
  #3  
Old 10-11-11, 02:52 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
If the fan is on AUTO, then for kicks, remove the G wire at the stat. If the fan stops, then it may be the stat. If the fan stays on, then go to the air handler, and remove G there.. If that stops, then you have a short in the wire. if it don't stop, then it's the air handler itself.
 
  #4  
Old 10-12-11, 12:43 PM
J
Member
Thread Starter
Join Date: Oct 2011
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
Looks like I found the problem, it was the delay time relay in the air handler. I replaced that and all is well
 
 