Luxaire model G9T10020UPC13C - blower (fan) unit will not run
I cannot get the fan unit (blower) to work in either heat or emergency heat. I have a hybrid heating system (heat pump/gas furnace). I even tried turning the fan "on" and "auto" on the thermostat and nothing happens. I cannot find a "reset" button on the fan motor? Does this unit have such a thing? Do I have an electrical problem somewhere?
I cannot get my heat pump or gas furnace (emergency heat) to work. Is that because the fan will not work either?
Any suggestions?
Thanks!
I cannot get my heat pump or gas furnace (emergency heat) to work. Is that because the fan will not work either?
Any suggestions?
Thanks!
#2
http://www.luxaire.com/PDFFiles/035-...001-B-0304.pdf
Check the low voltage fuse in your furnace. If it has popped check the outdoor unit for a low voltage short.
The short is commonly between the heatpump and the house if cause by a weed eater, dog or the sun.
It is also commonly the low voltage wire to the reversing valve or a pressure switch rubbing bare on a copper pipe inside of the heat pump.
Check the low voltage fuse in your furnace. If it has popped check the outdoor unit for a low voltage short.
The short is commonly between the heatpump and the house if cause by a weed eater, dog or the sun.
It is also commonly the low voltage wire to the reversing valve or a pressure switch rubbing bare on a copper pipe inside of the heat pump.