Electric Heat doesn't turn on - wiring question
Old 11-14-12, 04:52 PM
D
Heat Pump / AC unit is:
International Comfort Products
Model: PHAD24N1K4
Thermostat is: RobertShaw 9610
Connections are shown in the diagram below:
PROBLEM:
A/C Works, but Heater doesn't turn on. I noticed that on my heat pump terminal block, Y1 was jumper-ed to W1 and W2 and that didn't seem right, but A/C doesn't work if I disconnect W1 and W2.
It seems to me that the W on the T-stat should be connected to W1, and that Y on the T-stat should be connected to Y1 (and not jumpered to W1, W2). I tried that and then neither A/C nor heat worked. For now I have set it back to the wiring above and A/C works, but the heat does not.
I am hoping someone more expert than myself will see the problem here and suggest a simple solution.
Thanks!
Old 11-14-12, 04:56 PM
D
Here is a photo of the label from my AC / Heat Pump, and a photo of the A/C Terminal Block showing the jumpering from Y1 to W1 (W1 is jumper-ed to W2 on the back side):
Size:  24.5 KBName:  Chandler-20121113-00052.jpg
Old 11-14-12, 05:32 PM
hvactechfw's Avatar
Received 2 Votes on 2 Posts
Do you have aux (electric heat) or just the heat pump (no aux heat)? Your thermostat will not control aux heat. I can not find a manual for your unit. Can you post a picture of a schematic if you can find one on the unit?
Old 11-14-12, 06:17 PM
Received 1,113 Votes on 1,033 Posts
Thought I found wiring - wrong unit
Old 11-15-12, 09:52 AM
D
Wiring Diagram
I called the manufacturer and got them to send me a PDF version of the wiring diagram (see image). This matches the diagram on the unit, but it is a lot easier to read than my pictures.
Also found out that this is branded as an ArcoAire unit.
So correct information is:
Brand: ArcoAire
Model: PHAD24N1K4
When I googled ArcoAir
PHAD24N1K4 I was able to find a Users Manual with recommended thermostat wiring that is pretty close to what I have (see below). I marked it up to show my current configuration including the jumper between Y1 and W1 on the unit side. If I remove that jumper the A/C stops working.
Based on this diagram I am thinking that maybe I just need to jumper Y and W on the Thermostat side as shown in the Users Manual. Does that look right?
Old 11-15-12, 10:03 AM
D
Wiring diagrams that might be easier to read
PDF's have a 50k limit so I am posting this as an image. I assume you just need the connection diagram and not the Ladder diagram:
Old 11-16-12, 09:09 AM
D
Problem solved.