Hello,

I have a Ruud Heat Pump Air Handler, Model HQA, that is constantly running even when the outside Heat Pump is off. 2 weeks ago it started, I replaced the Thermostat and the unit began working appropriately. Today, the Heat Pump Air Handler, fan, and perhaps Emergency Heat ran all day. This evening I removed all of the wires from the tstat and the Heat Pump Air Handler and fan continued to run heating the rooms. I reconnected the tstat and turned the temperature up to make sure it was still able to control the outside unit, which worked as expected. I went up in the attic to check out the Heat Pump Air Handler and look for any signs of issues was surprised to see how clean everything looked for a unit that is 25 years old. Now that I believe I have eliminated the tstat as the issue, could this be a relay issue? If so, any idea which relay? I have included links to the pictures of the wiring in the heat pump air handler for reference. Your support is appreciated in advance.

20131121_221758 - Copy | Flickr - Photo Sharing!

20131121_221810 - Copy | Flickr - Photo Sharing!

Thank you
 
Sponsored Links
  #2  
Old 11-21-13, 11:18 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,254
Received 482 Votes on 452 Posts
Welcome to the forums.

You don't have a thermostat problem. You have a defective sequencer in the air handler. It's job is to turn on the fan and the heating coils. It is getting stuck on.
 
  #3  
Old 11-21-13, 11:29 PM
Member
Thread Starter
Join Date: Nov 2013
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Thank you PJMax! How would I go about replacing the sequencer in the air handler? Specifically where is the sequencer located in the air handler?
 
  #4  
Old 11-22-13, 02:04 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,254
Received 482 Votes on 452 Posts
I can't tell if there is one or two sequencers there.

Name:  bbb.jpg
Views: 2645
Size:  23.4 KB
 
  #5  
Old 11-22-13, 08:21 AM
Member
Thread Starter
Join Date: Nov 2013
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Hello PJmax,

Sorry for not taking another picture with a birds-eye view. I believe there are actually three sequencers there. I will need to take apart the unit again. In continuing to troubleshoot last night, I ran the tstat through the "cycles", pausing 20 seconds after each one (cool, heat, emergency heat, and off) when I ran through the cycle the second time, the tstat triggered the heat pump air handler to return to normal operations. I am sure it's going to stop working again, so I want to make sure I get the replacement parts soon and fix the issue.
 
  #6  
Old 11-23-13, 08:54 AM
Member
Thread Starter
Join Date: Nov 2013
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Hello PJmax, here is the top view of the picture you added an arrow to. It appears there are two sequencers?

20131123_103116 - Copy | Flickr - Photo Sharing!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On