I am trying to replace a old Honeywell T874G thermostat on a older York B1Sp042A06 Heat Pump unit. The low voltage wires on the old stat ate G,W,X,B,O,and Y
I am try to hook up a programmable Climatemaster stat (ATP32U03)
The connections on the new one are, C, R, W1, O, Y1, Y2, AND G
Any help would be greatly appreciated!!
Old 11-27-13, 03:39 PM
Houston204's Avatar
Received 17 Votes on 14 Posts
Post the Q674 number on the subbase.
Post all terminals on the old subbase as well to help locate your diagram.
Were all the terminals that you posted in use?
Old 11-27-13, 03:58 PM
G
Size:  37.3 KBthank you, in advance, for your help!!
yes, all the terminals stated are used.
the # is: Q674- J1027
Old 11-27-13, 04:52 PM
Houston204's Avatar
Looks like B is common.
Old 11-27-13, 05:04 PM
Houston204's Avatar
http://www.villagesatbelvoir.com/wp-...e6dfb53182.pdf
Old = New
G = G
W = W1
X = tape off
B = C
Y = Y1
Old 11-27-13, 05:15 PM
user 10's Avatar
Received 39 Votes on 33 Posts
You may have an outdoor t-stat which keeps part of the aux heat kit off above a certain outdoor temp.
On your system, X may activate a relay to bring on the entire set of heat strips in emergency heat mode.
You can tape X off for now, but emergency heat may not operate at full capacity.
Old 11-27-13, 06:47 PM
Houston204's Avatar
Every ODT that I have seen wires to the indoor unit. Disconnecting E at the stat shouldn't affect this.
Old 11-28-13, 09:17 AM
G
so I do not need to connect O,R or X to the new stat
thank you so much for all your help with this.
Old 11-28-13, 09:27 AM
Houston204's Avatar
Connect the old R to the new R.
Connect the old O to the new O.
The question is X. If you have 20 KW with 10 KW controlled by W and 10 KW controlled by X you will see a large jump in your light bill by connecting both W and X to the new W.
I would only connect the old W to the new W.
If you find that you are still cold, you can always add the old X to the new W later.
Old 11-28-13, 01:48 PM
G
Thank you so much for all your help, the stat is working perfectly!!
Old 11-30-13, 02:35 PM
user 10's Avatar
E may be connected to a relay to bypass the outdoor t-stat and bring on the entire heat kit regardless of outdoor temp in emergency heat mode.
I agree that it shouldn't affect normal heatpump operation.
Old 11-30-13, 03:26 PM
Houston204's Avatar
Interesting. Post a diagram with your wiring so that we can view it.
Old 12-16-13, 10:57 AM
G
I noticed that the condenser on the outside of the heatpump is frosting up, is this normal for this time of year? when it is very cool outside?
Old 12-16-13, 05:37 PM
Houston204's Avatar
Yes, this is normal. The heat pump has a defrost cycle to address this.