HELP York Heat Pump Fault Code "multiple limits on single call for heat"

I have a York Heat pump and air handler with auxiliary heat. Heat pump yzb03611
Air handler MA14DN21, Heater 4HK16501806
Ever since it was installed it has faulted on this code. There have been 5 so-called technicians look at it and they come up with ridiculous reasons for the problem. I decided to trouble shoot it myself and have done the following:
Sped up the fan, changed the main control board in the air handler, changed the two limit switches, tried disconnecting one set of heater elements. The problem happened a couple times in a heating season initially, it happened more and more and now faults every day. (fan runs continuously to indicate a fault). Is there anything in the heat pump itself that can cause this? I can't find a schematic for the heat pump
 
Sponsored Links
  #2  
Old 12-08-13, 07:05 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,410
Received 14 Votes on 11 Posts
Do you have the installation manual for your heat pump and air handler?
Post the manual numbers if you have them.
 
  #3  
Old 12-08-13, 10:02 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,166
Received 475 Votes on 445 Posts
  #4  
Old 12-09-13, 08:45 AM
Member
Join Date: Dec 2012
Location: United States
Posts: 246
Received 1 Vote on 1 Post
I have a similar system. The install manual for my air handler is here:

https://skydrive.live.com/redir?resi...nt=file%2c.pdf

I got this from the York website years back when they used to provide actual manuals rather than just advertising puffery.

You can see if it's the same control board, see pages 7,8,9 especially .
Maybe some other tips you can glean.

Also, do you get the faults if you operate in emergency heat - i.e. no heat pump.

I'm guessing that you've assured yourself of no blockage ... I had a similar problem which turned out to be a piece of the air handler sidewall insulation that had come unglued flapping into the air flow.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: