Heat pump keeps tripping pressure switch!

HP21-60-230-03 outdoor unit.
CB31MV-51 Air Handler.

I happens quite frequently. Ive reset it twice in the last week. I understand this can be related to 'air flow'. Not even sure what that means. Its a two speed unit and I have plenty of 'air flow' out of the vents. Is there something I can do to keep this from happening? Its done this for several years and the techs have verified the switch is functioning properly. What can I do to keep this from happening? Im about two 'trips' away from flipping on my emergency heat in the panel and calling it good for the rest of the winter. It does not do this on cooling mode (usually).

If its air flow, can I just increase the fan speed or something?

Im noticing this more now because I have new thermostats that do not call auxiliary heat until that absolutely HAVE to, that means this stat will run for an hour or more before kicking in, so I notice when its cold in teh house.
 
Sponsored Links
  #2  
Old 12-12-13, 09:59 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,522
Received 408 Votes on 384 Posts
I'm not following you..... reset the pressure switch ? Where would that be ?

You have a heat pump with electric reheat coils..... is that correct ?
 
  #3  
Old 12-13-13, 12:04 PM
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 370
Received 1 Vote on 1 Post
There is a switch in the outside unit that has to be reset if the head pressure on the compressor becomes too high. Maybe its temp based, but its soldered into the copper. So, it trips and the air handler will come on, but the compressor will not because you have to go outside and push the reset switch. Its to keep the compressor from exploding.

I have a heatpump with strip back up/aux.
 
  #4  
Old 12-13-13, 07:21 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,380
Received 10 Votes on 8 Posts
Does this heat pump have a motorized zone control (or bladder) system on it?
 
  #5  
Old 12-14-13, 02:35 PM
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 370
Received 1 Vote on 1 Post
It has a zone system on the ducts. It uses an Arzel system. Its a vacuum operated system. All of that seems to be functioning properly though. Thats the only zoning there is on the system and its not part of the heat pump.
 
  #6  
Old 12-14-13, 02:44 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,522
Received 408 Votes on 384 Posts
It may not be directly connected to the heat pump but if it restricts airflow across the evaporator coil.... that could be causing your problem.
 
  #7  
Old 12-14-13, 04:01 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,380
Received 10 Votes on 8 Posts
I agree with PJ.
This can be addressed with a barometric bypass which will dump air into a stairwell or some other "Neutral space" when half of the zones close.
 
  #8  
Old 12-15-13, 11:08 AM
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 370
Received 1 Vote on 1 Post
I have a bypass that dumps back into the air handler, but also I have a 'wild zone' that dumps into the living room no matter which zone is calling.

Its just wierd because it runs for 3 days.....5 days....or 1 day and then trips out. I cannot determine the exact parameters and temps that cause it. Its been running since I made this post without issue.
 
  #9  
Old 12-15-13, 11:21 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,380
Received 10 Votes on 8 Posts
Dumping hot air back into the return and running that air through your indoor coil is like running your AC on a 120 degree (or hotter) day.

Closing off 50% of the dampers without a bypass is like blocking half of the outdoor coil in the summertime while running cooling.

Carrier has a zone control that gives you "All Zones" as a control option.
That would be a great feature with this problem.

Is the indoor coil clean?
Are you using pleated filters that are very restrictive (3M)?
Theses factors could also contribute to this problem.
 
  #10  
Old 12-16-13, 07:32 AM
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 370
Received 1 Vote on 1 Post
Yes, the coils are clean. I have a media filter that is replaced every 6 months. I use fiberglass filters in my return register to catch big stuff and prolong the life of the media filter in the air handler.

I do have an option on my board to open all zone dampers. So far, its still running without issue. I really don't know what causes it, sometimes it does it, sometimes it doesnt, but I think your assessment of dumping hot air back into the coil is right on.


When she dies, it will be the last heat pump my house has.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: