I have a 3 ton goodman split system heat pump that was installed towards the end of summer last year... it cooled great and when it came time to switch it to heat mode it heated great until about a month ago... while in heat mode the suction line gets hot like its suppose to then after a few minutes it changes to just luke warm and finally got ice cold like it was trying to cool... I have checked the wiring connections and they all seem to be fine... what would be causing this?? could it be that the reversing valve has went bad?? what can I do to check the reversing valve? the fact that the line gets hot then gets ice cold, wouldn't that mean the compressor is okay?? thanks so much in advance for help!
 
Sponsored Links
  #2  
Old 02-05-14, 05:45 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
Sounds like you should still be under first year warranty. This option is the best choice if you paid for this installation.

If this is not an option...

It seems more likely that you have a refrigerant leak than a failing reversing valve but you can verify that 24 volts is not present at the reversing valve by unplugging it.
 
  #3  
Old 02-06-14, 06:24 AM
R
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
Thanks for replying! Ive read that the reversing valve isnt energized in the heating mode and if so wouldnt that eliminate that as a possible problem? What do u think would cause this ? Thank u so very much.
 
  #4  
Old 02-06-14, 04:54 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
You might have a short between O and R or between O and Y.

I'd measure for 24 volts AC between O and C to prove that voltage is not present but you can just unplug the reversing valve if you do not have a meter.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: