Heat pump fan not coming on

The unit tried to start up and then we heard a humming but the fan would not kick in. We could smell like electrical smell. Found capacitor had leaked liquid. We replaced the cap and the unit would run constantly and not shut off when it reached it temp on stat 68. I lowered stat to 55 and it seem to work right. Tonight it went to start up and it did it again started humming and would not come on. Outside unit came on. Same smell. What is wrong? It has been very cold here in Va.
 
Sponsored Links
  #2  
Old 02-28-14, 07:23 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
Heat pumps can have a separate capacitor for the compressor and fan or a dual capacitor to serve both. If you have a dual capacitor the wiring arrangement is important.

Did you replace a dual capacitor? If not, you may have a second cap that may require replacement.

If you post the make and model number, we may be able to bring up a wiring diagram.
 
  #3  
Old 02-28-14, 07:35 PM
S
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
It is a Trane tweo36c140b0 Date 2001
 
  #4  
Old 02-28-14, 08:01 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
http://www.trane.com/webcache/un/spl...5_04012001.pdf

Okay, this is an air handler. Are you getting 240 volts AC between red and black to the motor?

 
  #5  
Old 02-28-14, 08:25 PM
S
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
I have no tester right now to test it. When it was starting it didn't seem to drag or act like it was a struggle. The capacitor I replaced has only lasted 1 1/2days when humming started again. I read that a faulty relay could cause capacitor to stay engaged longer than needed and overheat it. I may have to get some one to come look at it cause I know nothing about these but was hoping for a quick fix. Question. does it matter what type of filters you use. We always used the blue thin see thru type, and now tried the newer ones that you can,t see thru. Can that slowly cause a problem?
 
  #6  
Old 02-28-14, 10:41 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
It is unlikely that your filter selection has any impact on the motor failure.
A start relay must take a start capacitor out of the circuit after startup but your air handler motor does not use a start cap. It uses a run capacitor which stays in the circuit the entire time that the motor runs.

It is probably going to be the FDR (fan delay relay) or the motor if you correctly installed the correct capacitor for the motor. A voltage measurement to the motor should help determine which.
 
  #7  
Old 02-28-14, 11:12 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
Thank you.
I wish that I could communicate as well to my customers on a daily basis.

Yep, I think it's broke...
 
  #8  
Old 03-01-14, 05:18 AM
S
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Question

Thank you. Where would the FDR be located?
 
  #9  
Old 03-01-14, 06:39 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
This diagram show a red wire from the motor connected to the FDR.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: