Carrier Condensor Fan
Unit: 10-15 year old Carrier Heat Pump Model: 38YCA048300
Symptoms: Condensor Fan was squelling (at times) and running sporadicly. Motor had tons of in/out play in the shaft.
Repairs: Replaced fan motor and dual run capacitor.
Continuing issue: Can't figure the off/on sequence of fan motor. The heat pump seems to operated correctly but the fan will shut down during normal run mode (house heating). I can't say that i've been able to nail down a pattern but have seen it stop after about five minutes of running. The fan does not seem to run during the defrost cycle. Been too cold to test in cooling mode.
Could it be: The defrost thermostat. The whole unit has been icy - the coils are defrosting fast during the cycle but the bottom of unit gets very iced-up due to the runoff refreezing. The defrost thermostat looks to be on a coil at the very bottom of the unit where ice builds up. Symptoms seems to remain the same on days warm enough to melt away the buildup.
Thanks
Symptoms: Condensor Fan was squelling (at times) and running sporadicly. Motor had tons of in/out play in the shaft.
Repairs: Replaced fan motor and dual run capacitor.
Continuing issue: Can't figure the off/on sequence of fan motor. The heat pump seems to operated correctly but the fan will shut down during normal run mode (house heating). I can't say that i've been able to nail down a pattern but have seen it stop after about five minutes of running. The fan does not seem to run during the defrost cycle. Been too cold to test in cooling mode.
Could it be: The defrost thermostat. The whole unit has been icy - the coils are defrosting fast during the cycle but the bottom of unit gets very iced-up due to the runoff refreezing. The defrost thermostat looks to be on a coil at the very bottom of the unit where ice builds up. Symptoms seems to remain the same on days warm enough to melt away the buildup.
Thanks
#6
Member
Thread Starter
Join Date: Jul 2012
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
They are not visibility dirty - have been cleaned in the past. I will clean the coil this weekend when the weather warms.
Would only the fan shut off and the compressor run on?
Would only the fan shut off and the compressor run on?
#9
Member
Yes the internal overloads. If there is not enough air flow the motor will heat up. As for the defrost thermostat, I would mount it right past the TXV (Thermostatic Expansion Valve).
On a heat pump the fan wire is run through the defrost board to stop the fan in defrost mode. It is possilble that the defrost module is faulty and turning the fan off.
On a heat pump the fan wire is run through the defrost board to stop the fan in defrost mode. It is possilble that the defrost module is faulty and turning the fan off.
#10
I have not read anything about the unit not heating in this thread.
If it is heating fine then this is the normal operation of a heat pump as PJ has already posted.
If you Google heat pump defrost cycle video, it might help.
If it is heating fine then this is the normal operation of a heat pump as PJ has already posted.
If you Google heat pump defrost cycle video, it might help.