Heil furnace circulating fan stays on

model mf 12F1900A2
circulating fan stays on even when thermostat is removed, when I turn off switch at main panel fan goes off for awhile, then it will cycle on and off and then stay on. I replaced the control fan timer, didn't help. I removed all control wires to the control module, the fan still stays on.
 
Sponsored Links
  #2  
Old 04-12-14, 07:52 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
http://icpindexing.toddsit.com/docum...4201220501.pdf

That diagram looks alot like Carrier's.
What heat strip do you have installed in this unit?

Do you have a sequencer installed? They often cause this problem...
 
  #3  
Old 04-12-14, 09:08 PM
R
Member
Thread Starter
Join Date: Apr 2014
Location: United States
Posts: 3
Received 0 Votes on 0 Posts
it has a AMFK20DHB1 heating unit, no sequencer installed
 
  #4  
Old 04-13-14, 10:51 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 58,569
Received 1,041 Votes on 965 Posts
Looks like the blower is controlled strictly from the fan control board.

Name:  heat.jpg
Views: 1771
Size:  39.1 KB
 
  #5  
Old 09-03-14, 08:22 AM
C
Member
Join Date: Jun 2014
Location: Canada
Posts: 3
Received 0 Votes on 0 Posts
I agree with the comment that fan is be controlled from the control board so if you’ve removed the board, how is the fan still getting a signal. Such situations usually demand reverse engineering, not the fan but the circuitry. It is important that you need to follow the control signal. You can use the multi-meter and see where the control signal is connected to. This will certainly clarify how your fan works.
 
  #6  
Old 09-03-14, 09:37 PM
R
Member
Thread Starter
Join Date: Apr 2014
Location: United States
Posts: 3
Received 0 Votes on 0 Posts
After turning off main switch at the furnace for about the fifth time, which was after I replaced the control module, the fan started to work properly. Thanks.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: