Heat Pump Contactor Not Pulling In
#1
Member
Thread Starter
Join Date: Feb 2014
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Heat Pump Contactor Not Pulling In
The inside air handler comes on when the thermostat calls for COOL but the outside unit not starting. I can actually hear and see the contactor try to pull in but not pulling in. If I manually push in the contactor everything works fine fan turns and compressor comes on but if I release it stops working. I have my HVAC EPA license and work for an apartment complex, just need a little advice of whats causing this? I am thinking that it may be the transformer in the air handler not working properly.
#2
Member
Put your meter on the contactor coil. If you have 24V, then the contactor is bad. If 0 volts, check from R to C and Y to C in the furnace.