Heat Pump Contactor Not Pulling In

The inside air handler comes on when the thermostat calls for COOL but the outside unit not starting. I can actually hear and see the contactor try to pull in but not pulling in. If I manually push in the contactor everything works fine fan turns and compressor comes on but if I release it stops working. I have my HVAC EPA license and work for an apartment complex, just need a little advice of whats causing this? I am thinking that it may be the transformer in the air handler not working properly.
 
  #2  
Old 08-02-14, 01:07 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Put your meter on the contactor coil. If you have 24V, then the contactor is bad. If 0 volts, check from R to C and Y to C in the furnace.
 
  #3  
Old 08-11-14, 07:21 AM
M
Member
Join Date: Aug 2014
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
If you check for 24 volts and your voltage disappears you have a bad connection in a wire nut or bad t-stat wire
 
 