Heat pump not powering on

Hi, would appreciate any help. A/C quit last night, went out to check today. Capacitor looks good. Noticed a small #3 blade fuse blown and replaced w/ no luck. Seen some other posts here about a contactor? Seems to be a possible reset button in middle on it (think I'm at right component) where the main power leads are attached. When I push in button, unit kicks on but back off when I release it. Is this possibly my problem? Thanks for any help
 
Sponsored Links
  #2  
Old 09-23-14, 06:59 AM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,727
Received 0 Votes on 0 Posts
It sounds like you either lost 24V to the contactor or the contactor coil is bad. Do you have a multimeter to test for voltage at the contactor? When you replaced the 3 amp fuse are you sure it didn't blow again? It will blow due to a wire with a bare spot (usually caused by rubbing on metal where it passes through openings) rubbing and causing a short to ground. Sometimes homeowners damage the thermostat wires between the house and the condenser while using a weed-eater or dogs chew on the wires. I suggest you check the fuse again and inspect those wires outside by the condenser to look for damage or a bare spot on the wires.
 
  #3  
Old 09-23-14, 07:05 AM
M
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
Thanks for your reply, fuse is good. Spring loaded contact looks burnt though. Looks like power wire was shoved in a little too far. I have a voltmeter but not sure where to begin testing. No dogs to chew wires and haven"t done any weed eating in a week or so. Thanks
 
  #4  
Old 09-23-14, 07:12 AM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,727
Received 0 Votes on 0 Posts
The fact that the contactor looks burnt points to that as the root of your issue. I have attached a diagram with the basic test points at the contactor. Turn the thermostat to well below room temperature. Set you multimeter to volts AC and test voltages ACROSS L1 and L2, T1 and T2 and the 24V on the side of the contactor. Some contactors have the 24v terminals on the same side. Use extreme caution as the voltages are lethal.
 
Attached Images  
  #5  
Old 09-23-14, 07:46 AM
M
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
Yeah, electricity scares me as I'm not a electrician. Cut all power and removed contactor and capacitor, going to parts store in a few, will advise on result. Thanks firedawg
 
  #6  
Old 09-23-14, 02:55 PM
M
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
Success!!!!! New contactor did the trick, also took capacitor to hvac parts store to have checked and it was good. Thanks for help earlier Firedawg
 
  #7  
Old 09-23-14, 03:05 PM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,727
Received 0 Votes on 0 Posts
Great job! Glad you got it back in service and thanks for the update.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: