Condenser fan starts and stops intermittently.

Rheem condenser fan starts and stops intermittently in heat mode. Old fan burned out. Replaced fan and cap( old was good). Replaced defrost control. Still does it.
 
Sponsored Links
  #2  
Old 12-10-14, 04:08 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 57,678
Received 913 Votes on 853 Posts
Welcome to the forums.

It is normal for some condensor fans to run intermittently when in heatpump (heat) mode.

How was the fan when in A/C mode ?
 
  #3  
Old 12-10-14, 04:11 PM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,727
Received 0 Votes on 0 Posts
Welcome to the forum!! The best place to start is to test the contactor wiring to see if the required voltages are present. Also, inspect the wires for burnt terminals. The attached diagram shows the points that voltages need to be tested. The meter needs to be on the volts AC setting and all tests done ACROSS the leads. These tests need to be with power on so extreme caution is required due to lethal voltages present. The contactor may look different, but test points are the same. To better assist, please post model number of condenser.
 
Attached Images  
  #4  
Old 12-10-14, 04:12 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
The outdoor fan motor should turn off when a heat pump enters defrost mode.
You should also hear the swish of pressure release as the reversing valve switches over when a heat pump enters defrost mode.

Is it possible that this is what your see?

What is the model number of your heat pump?
 
  #5  
Old 12-10-14, 04:13 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
Wow, I should learn to type with more than 2 fingers.
 
  #6  
Old 12-10-14, 04:29 PM
S
Member
Thread Starter
Join Date: Dec 2014
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
Rheem model RPLA-31jaz. Seemed fine during ac season. Just noticed this change a few days ago. It is not a variable speed system . 12 years old. 180/65 pressure with 70 room temp and 45 outside. Only thing I have not checked is a loss of voltage while it runs. Fan runs for 2 minutes then shuts off for 8 with compressor running. Not in defrost.
 
  #7  
Old 12-12-14, 10:44 AM
K
Member
Join Date: Dec 2014
Location: usa
Posts: 19
Received 0 Votes on 0 Posts
Your defrost board sends power to the fan motor, but more likely the capacitor is faulty or weak, weak capacitors cause low airflow and possibly cause the motor to overheat. If the cap has been weak for a long time it could cause the bearings to fail. If your not comfortable working on high voltage call a pro. If you can prove power is off, finding the exact capacitor and replacing it should not be hard.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: