Question on Mini Split in Heat Mode

Every half hour or so (haven't timed it exactly) my Mitsubishi cycles the directional vanes upward and seems to quit heating for a few minutes. It makes some small popping/creaking noises. Then it returns to normal. Is this usual and what is it doing?
 
Sponsored Links
  #2  
Old 01-21-15, 01:24 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 34 Votes on 26 Posts
Next time it happens go outside and look at the condensing unit, I'll bet it is in defrost mode.
 
  #3  
Old 01-21-15, 01:44 PM
H
Member
Thread Starter
Join Date: Mar 2008
Location: Boulder, CO
Posts: 1,101
Received 3 Votes on 3 Posts
Thanks, but what do I look for at the condenser? Will the compressor be shut down? The thing is so quiet that I don't know if I could tell.
 
  #4  
Old 01-21-15, 01:47 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 34 Votes on 26 Posts
The fan will not be turning and there will likely be a puddle of water under it. You might even see some frost on the fins.
 
  #5  
Old 01-21-15, 02:05 PM
H
Member
Thread Starter
Join Date: Mar 2008
Location: Boulder, CO
Posts: 1,101
Received 3 Votes on 3 Posts
When I got there, the fan was running, but the discharge air didn't feel much colder than ambient (27). I am curious now, how does this unit defrost? I vaguely understand that in heat mode the AC condenser must become the evaporator and be colder than ambient to extract heat.
 
  #6  
Old 01-21-15, 03:00 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 34 Votes on 26 Posts
My experience with a Mr. Slim was fifteen years ago and that one never went into defrost mode so what I will describe is more generic.

There is a temperature sensor attached to the coils of both the inside and outside units. When in the heating mode the sensor on the outside coil looks for something around 32 degrees and when it "sees" this it will switch the reversing valve and put the inside unit in cooling mode. This is why the direction vanes will move to direct the airflow to the ceiling, to prevent blowing any cold air on the room occupants. The defrost cycle only lasts a very short time, maybe even less than a minute in some cases, and then it reverts back to the heat mode.

What you are experiencing is completely normal.
 
  #7  
Old 01-21-15, 03:18 PM
H
Member
Thread Starter
Join Date: Mar 2008
Location: Boulder, CO
Posts: 1,101
Received 3 Votes on 3 Posts
Thanks Furd

I caught it right when the vanes started moving on the next cycle and rushed outside. The fan was off. That is clever how they cycle the vanes into AC mode for the defrost cycle.

Where I am still confused is that it can't defrost upon sensing 32 because this baby will produce heat down to near zero outside, so the outside evaporator coil must be going below zero at times. I suspect it is really hogging the power in that condition.
 
  #8  
Old 01-22-15, 07:06 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 34 Votes on 26 Posts
I don't know the exact method of determining when the outside coil needs to be defrosted. Sorry.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: