Coleman/york heat pump compressor not starting
#1
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Coleman/york heat pump compressor not starting
I have a 3 ton Coleman heat pump that was freezing up. Had a friend who is in heating and air look at it, he said defrost board was bad, we replaced that. It ran fine for about 5 hours, tripped the breaker and would not come back on. He came by and looked at it again, depressed the contactor and the fan motor would come on but the compressor would not. He tested the coil and it tested ok. He thinks my compressor is bad and needing replaced.
Just trying to get a 2nd opinion and see if any one had ideas as to any other issues that could cause this?
Thanks in advance.
Just trying to get a 2nd opinion and see if any one had ideas as to any other issues that could cause this?
Thanks in advance.
#2
Welcome to the forums.
A second opinion..... not a good friend I guess.
If you manually push the contactor in and only the fans starts.... it would indicate a compressor problem. If it was a start capacitor issue you would hear the compressor hum loudly when trying to start.
Some compressors have a heat band around them to keep the oil warm when the temps get cold. That could possibly be a cause of the problem if one is present and burned up.
A second opinion..... not a good friend I guess.

If you manually push the contactor in and only the fans starts.... it would indicate a compressor problem. If it was a start capacitor issue you would hear the compressor hum loudly when trying to start.
Some compressors have a heat band around them to keep the oil warm when the temps get cold. That could possibly be a cause of the problem if one is present and burned up.
#3
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
No, not that at all, he is a very good friend I just always like to get a 2nd opinion, especially when it comes to spending money
So that heat band could be the problem, even though it was about 45 degrees when we were messing with it yesterday?

So that heat band could be the problem, even though it was about 45 degrees when we were messing with it yesterday?
#4
That is when a crank case heater would be energized. The wires to a crank case heater can melt ,often near the compressor, and trip the breaker.
If it checks out okay, I would turn off the breaker to the outdoor unit and inspect the compressor terminals...

Measure the capacitance of the compressor run capacitor...

Get an ohm reading across the compressor terminals and measure each terminal to ground.
If it checks out okay, I would turn off the breaker to the outdoor unit and inspect the compressor terminals...

Measure the capacitance of the compressor run capacitor...

Get an ohm reading across the compressor terminals and measure each terminal to ground.

#5
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Had a capacitor on hand so i stuck it on. Turned the unit back on and it would not start, but when the contactor was depressed again, the compressor and fan both kick on. Is this a bad contactor or could it still be a compressor issue?
Thanks
Thanks
#7
The first post said that the compressor would not start when you depressed to contactor manually?
What size capacitor did you take off, and what size capacitor did you install?
I would check the pressure switch connections to the defrost timer.
What size capacitor did you take off, and what size capacitor did you install?
I would check the pressure switch connections to the defrost timer.