Lennox AHU/Heat Pump, Honeywell T-stat wiring

Reply

  #1  
Old 03-11-15, 10:56 AM
D
Member
Thread Starter
Join Date: Mar 2015
Posts: 1
Received 0 Votes on 0 Posts
Lennox AHU/Heat Pump, Honeywell T-stat wiring

I want to make sure my low voltage wiring is connected correctly. Here's what I have:
2-ton CBX32MV, 8 KW 1-stage heat strip, 2-stage XP16 Heat Pump
3-ton CBX32MV, 9 KW 2-stage heat strip, 2-stage XP16 Heat Pump
Honeywell VisionPro TH8320U Thermostats

AHU wiring diagram:
Name:  CBX32MV wiring.jpg
Views: 7297
Size:  39.9 KB

T-stat wiring diagram:
Name:  th8000 wiring.JPG
Views: 6909
Size:  29.6 KB

Question:
The T-stat has a single Aux/E terminal. Does this connect to the W1 terminal for both units and keep the factory jumper from W1-W2 & W-2-W3? In the CBX32MV install manual, it says to "Remove jumper between W1 & W2 for two stage electric heat." I have 3 stages of heat right so I keep it in?

Thanks
 
Sponsored Links
  #2  
Old 03-11-15, 07:00 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
I would keep the jumper in place for an 8 or 9 KW heat strip. It wouldn't be enough to make me upgrade the stat. If you had 15 or 20 KW the difference in operating cost would pay for the stat.

The Honeywell Prestige IAQ could take advantage of that DS terminal and take advantage of separate stages of electric heat strips.

It is too bad that they didn't install the VisionPro TH8321R. You could have upgraded for the cost of an EIM.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: