Change 1F89-273 White-Rodgers to Honeywell Pro 3000 wiring help
#1
Member
Thread Starter
Join Date: Dec 2015
Location: USA
Posts: 1
Received 0 Votes
on
0 Posts
Change 1F89-273 White-Rodgers to Honeywell Pro 3000 wiring help
I have the following wiring terminals and old connections to the WR thermostat. Which wires go where on the Honeywell?
W-R Wire PRO
R brown R
G green G
O orange O
Y white/green Y
C blue C
L (none) L
W2 white/brown B
E white/blue E
AUX
Thanks.
W-R Wire PRO
R brown R
G green G
O orange O
Y white/green Y
C blue C
L (none) L
W2 white/brown B
E white/blue E
AUX
Thanks.
#2
Welcome to the forums.
The wiring you are describing is data/phone cable. Eight conductor cable like CAT 5 computer cable.
That cable is #24 wire when #18 thermostat cable is suggested/required.
A short run is passable but it makes the wiring confusing.
I'll be back with the wiring code.
The wiring you are describing is data/phone cable. Eight conductor cable like CAT 5 computer cable.
That cable is #24 wire when #18 thermostat cable is suggested/required.
A short run is passable but it makes the wiring confusing.
I'll be back with the wiring code.
#3
PRO 3000 is the product category not the model number.
From what I see you cannot use a stat in this series. You need a stat that can control a heatpump system with back up electric heating.
From what I see you cannot use a stat in this series. You need a stat that can control a heatpump system with back up electric heating.
#4
You cannot connect anything to the B terminal on the new thermostat.
The old W2 is the new Aux.
https://customer.honeywell.com/resou...0s/69-1775.pdf
I recommend pulling new stat wire or using a redlink TH8321R thermostat with an EIM so that you can lose that cat 5 wire.
The old W2 is the new Aux.
https://customer.honeywell.com/resou...0s/69-1775.pdf
I recommend pulling new stat wire or using a redlink TH8321R thermostat with an EIM so that you can lose that cat 5 wire.