Goodman aruf blower not turning off in heating mode
#1
Member
Thread Starter
Join Date: Apr 2016
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Goodman aruf blower not turning off in heating mode
Blower shuts off in cooling when tstat is satisfied ,but not in heating? Could this be a sequencer problem.
#2
#4
If it turns out to be the sequencer.... take pictures of the wiring so that it gets reconnected correctly. It's very easy to get the wiring mixed up.
#5
It could also be a thermostat B terminal issue.
Have you replaced the thermostat recently?
Is a wire on the thermostat B terminal?
Have you replaced the thermostat recently?
Is a wire on the thermostat B terminal?
#8
The B terminal is energized the entire time the thermostat is in heat mode regardless of the temperature setpoint.
#10
The sequencer is the most likely cause if the thermostat has not been recently replaced.
The B terminal should not have a wire connected to it at the stat. If the thermostat has recently been replaced it is very possible that this is the issue.
The B terminal should not have a wire connected to it at the stat. If the thermostat has recently been replaced it is very possible that this is the issue.